Dont understand instructions clearly, another forum member has just forwarded me the instructions and still confused?

When taking Ze reading the meter only seems to show the pscc value but not pfc value.

As I read the instructions it only seems to give you the pfc option on the Zs(Zloop) setting and pscc on the Ze(Zline) ?? confused me. Can anyone tell me otherwise or am I misunderstanding the instruction manual.
(probably the latter)
 
When you measure the external earth fault loop impedance, ze, using the Zloop function you are measuring the resistance between Line and Earth at the origin.
When you measure the earth fault loop impedance, zs, of a circuit with an RCD in place you use the zRCD function, this is again measuring the resistance between Line and Earth but with the tested circuit included.

In both these cases the Isc value given is the Prospective Earth Fault Current, PEFC

When you measure the prospective short circuit current using the zLine function you are measuring the resistance between Line and Neutral and the Isc value given is the Prospective short circuit current, PSCC.

The highest of the PEFC and PSCC is the Prospective Fault Current, PFC.
 
Liddley remember GN3 requires:- Ze is measured with the earthing conductor disconnected from the MET. Whereas Zs, PSCC and PEFC are all measured with the earthing conductor connected to the MET.
In practice, when testing for Ze with the earth conductor disconnected from the MET your MFT will provide you with readings for both Ze and 'PEFC' from this test, however, the 'PEFC' reading should be ignored. When the earthing conductor is reconnected to MET the test is repeated this time ignoring the 'Ze' value, which is likely to be lower than previous one due to parallel earth paths, consequently PEFC is likely to be higher and the worst case value which should be noted and compared with PSCC later in order to determine the PFC to be recorded on the paperwork.
 
Last edited by a moderator:

Reply to Anyone got a Metrel 3125 Eurotest Combo in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock