Course they do, they forget to disconnect any parallel paths.::
On the 13 ohms I mentioned, with bonding connected to gas and water supplies, when i took the measurement again, the Ra had dropped to 0.3 or there abouts
No seriously E54, i'm being genuine.
Zs at origin then i suppose.
Yes, you're right E54. Its only 3 small cottages that are TT, for some reason everything else has been converted at some point.
Water is still supplied in lead which pretty sure won't have any corrosion protection applied.