Course they do, they forget to disconnect any parallel paths.:o_O:

On the 13 ohms I mentioned, with bonding connected to gas and water supplies, when i took the measurement again, the Ra had dropped to 0.3 or there abouts


That would be Zs!! And i doubt very much that any bonding would pull your Zs down to 0.30 ohms. ....Not unless someone down the street has a PME connection, as both the water and gas main pipes generally have an underground protective anti corrosion covering...
 
No seriously E54, i'm being genuine.

Zs at origin then i suppose.

I don't disbelieve you, far from it. But there will be a reason for that dramatic fall in your Zs values, and the most likely one being PME connections along the street. Be they official or unofficial PME connections. ..lol!!
 
Yes, you're right E54. Its only 3 small cottages that are TT, for some reason everything else has been converted at some point.

Water is still supplied in lead which pretty sure won't have any corrosion protection applied.
 
Yes, you're right E54. Its only 3 small cottages that are TT, for some reason everything else has been converted at some point.

Water is still supplied in lead which pretty sure won't have any corrosion protection applied.


You say that, but my parents house had a lead water supply, when we came to add an extension and dug out for the foundations, that lead pipe had a DENSO type tape (Grease impregnated tape, ..horrible stuff) wrap!!
 
Oh yes, know the stuff well. Takes days to clean your hand up after using it!

Its just from other experiences really with working in close proximity to this place. Other houses have alterations done and only ever seen the lead naked in the ground.

Know what you mean though
 

Reply to Best ZE on TT in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock