Alright,

im currently testing a store and come across a situation I'm a little unsure on. I've got 3 4c SWAs feeding 3 different boards, no separate earths with any of them and no fly leads from banjos to the DB their feeding or supplied from, there relying on the trunking and chassis of the main panel to get their earth, zs fine etc, so would this be a c2 or a c3 in ur opinion
 
Difficult one I would say C2 No I'll edit that and say C3 improvement recommended
 
I would say C3 as well, although I am not sure which reg would back me up on that.

If your ZDB readings are within the limits, by fitting a link from the banjo to the earthing bar should improve the readings, not got my 7671 handy so can't help with a reg noView attachment Best-Practice-Guide-2.pdf think Ive got the right one attached sorry wrong one, try looking at the best practice guide for EICRs on google cant seem to get my copy to attach
 
Last edited:
The OP hasnt mention the armourings not being suitable though, just no fly leads from gland to earth terminal. So i imagine this has been checked and complies with the regs.
 
The OP hasnt mention the armourings not being suitable though, just no fly leads from gland to earth terminal. So i imagine this has been checked and complies with the regs.

He says, "No separate earths", which I'm reading as no separate CPCs.
I reckon the armour sizings haven't been checked! :)
 
If the gland is attached to clean metal rather than painted then I see no issue.
If the glands are onto painted metal the only contact may be through the rough edges of the hole, this will give a good reading with the low current of a test.
However under fault conditions a much higher current will flow and if the metal to metal contact is not good enough then it's going to get very very hot!
 
Generally speaking you can safely say that any SWA cable up to 95mm be they 2,3, or 4 core will comply with CPC requirements, only excessive cable lengths can make a difference. However if any of these Sub DB boards are acting as EMT connections for bonding purposes then, i can almost guarantee that the steel armouring will not comply!!

Think everything else has been covered by others above!!
 
Unless they're huge cables where the armour is insufficient.
Where's that table?

Here you go, ....Again... lol!!



Remember these tables are relating to compliance for CPC, they are not to be seen as compliance for bonding purposes!!

Blue = min CSA of cables SWA to comply.

(Red) = Cable does not comply.

Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.

Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
15
16
17
2.5
5.7
17
19
20
4
9.0
21
23
35
6
13.6
24
36
40
10
22.6
41
44
49
16
36.1
46
50
72
25
36.1
60
66
76
35
36.1
66
74
84
50
56.4
74
84
122
70
79.0
84
119
138
95
107.2
122
138
160
120
135.3
(131)
150
220
150
169.2
(144)
211
240
185
208.6
(201)
230
265
240
270.6
(225)
(260)
299
300
338.3
(250)
(289)
(333)
400
403.9
(279)
(319)
467



Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.

Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
16
17
18
2.5
5.7
17
19
20
4
9.0
19
21
23
6
13.6
22
23
36
10
22.6
26
39
43
16
36.1
41
44
49
25
36.1
42
62
70
35
36.1
62
70
80
50
56.4
68
78
90
70
79.0
80
90
131
95
107.2
113
128
147
120
135.3
(125)
141
206
150
169.2
(138)
201
230
185
208.6
(191)
220
255
240
270.6
(215)
(250)
289
300
338.3
(235)
(269)
(319)
400
451.0
(265)
(304)
452
 

Reply to C2 or c3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock