Currently reading:
Cable size for main entry to house.

Discuss Cable size for main entry to house. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

H

Harry M

Hi,
Main supply cable entering my house is swa and measures 13.75mm outside diameter, don't know how many cores. I have electric wet central heating with a 9kw boiler plus immersion heaters, dishwasher, washing maching etc. all the normal stuff. House is all electric, no gas supply available here. Worry is the main cable looks small. Looking for some opinions from those more knowledgable than myself.
 
most likely be 16mm concentric cable. if DNO think that's good enough to fedd a 100A supply, then it;s good enough for me.
 
DNO will have supplied an appropriate service fuse to protect their cable.

You could always ring and enquire, although be prepared for a lot of faffing around.
 
Yes, cable is protected by standard 100 amp fuse. Became curious when main entry cable appeared to be smaller than 6mm2 swa I'm planning to use to supply a new garage. Concentric cable not something I've come across and may explain it. Thanks.
 
Straight Con = Combined N/E and only usable by DNO. Is that correct?

Not really, but 99% of the time, it would only be the DNO's using a concentric cable as a combined N-E cable!! They use split concentric as well, when replacing a damaged TN-S PILC cable, where the system hasn't been PME'd...
 
Not really, but 99% of the time, it would only be the DNO's using a concentric cable as a combined N-E cable!! They use split concentric as well, when replacing a damaged TN-S PILC cable, where the system hasn't been PME'd...

I see what you mean, when used by the DNO they use the outer conductors as a combined N/E cable but only they are allowed to do this.
We could of course use it in the same way as a 2 core cable, as long as the CPC function that it is lacking is provided for by other means.
Which is why I was wrong to say only the DNO can use it.

Cheers
 
I see what you mean, when used by the DNO they use the outer conductors as a combined N/E cable but only they are allowed to do this.
We could of course use it in the same way as a 2 core cable, as long as the CPC function that it is lacking is provided for by other means.
Which is why I was wrong to say only the DNO can use it.

Cheers

An example would be as a sub-main cable to an outbuilding on a TT system, where the earthing is being provided by roded systems. Only thing is, the cable, if taken underground would need to be ducted as they do not conform with BS7671 as a direct buried cable having no additional mechanical protection. The DNO's don't have to comply with BS7671, but even they only use it in the short lengths from the street distribution cable joint, to the their service heads!!

In reality, a straight concentric cable is rarely used outside of the DNO arena....
 
Not tough enough to stop a sharp stone or other debris getting through it, in a direct burial installation, nor a shovel or garden fork come to that!! lol!!
 
So you've not had a play with the new stuff the DNO's are installing. For BS7671 it isn't compliant but believe me it’s as tough as old boots.
 
So you've not had a play with the new stuff the DNO's are installing. For BS7671 it isn't compliant but believe me it’s as tough as old boots.

No, haven't touched the stuff for quite a while now Tony!! lol!! Not a real lover of the cable myself, it can be a real pain getting respectful end terminations, that don't look as if it's been installed by a 1st year apprentice!! The DNO don't have that problem, they just split it in the service head willy nilly, no-one ever see's the state of it!! lol!!
 
no-one ever see's the state of it!! lol!!


only when you pull the fuse, which, of course, you never do. LOL.


 
no-one ever see's the state of it!! lol!!


only when you pull the fuse, which, of course, you never do. LOL.



Not even then, in most of the service cut-outs i've seen!! Generally terminated (if you can call it that) in the square case below the fuse carrier!! lol!!
 

Reply to Cable size for main entry to house. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock