Hi All,
I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by overhead cable, however, this is in the way of the build. Rather than having the cubicle moved before the build and then again once the build is complete with the overhead cable buried, the DNO suggested looking at having their service cut out moved about 80 meters away to the top of the hill, and then power is taken down to the house by "any electrician". This removes the need for DNO involvement once the house is complete and gets rid of the overhead cable that they don't want to look at out of their window.
Having done the manual cable size calculation from Appendix 6 I am coming out at a 50mm2 cable for 100 amps over 80 meters. This drops 6 volts over the run. [in the calculation I am using a soil resistivity of 1.2 as the ground is wet clay even in summer as there is a lot of groundwater, giving a rating factor of 1.4 for direct buried SWA]. This obviously is pretty close to the 3% limit for total voltage drop for any lighting circuits.
I am planning on protecting the SWA with a 100amp cartridge fused switch. The consumer unit would be down in the house which will have a pretty standard install.
Questions I Had (Any help/advice appreciated)
Thanks
A.
I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by overhead cable, however, this is in the way of the build. Rather than having the cubicle moved before the build and then again once the build is complete with the overhead cable buried, the DNO suggested looking at having their service cut out moved about 80 meters away to the top of the hill, and then power is taken down to the house by "any electrician". This removes the need for DNO involvement once the house is complete and gets rid of the overhead cable that they don't want to look at out of their window.
Having done the manual cable size calculation from Appendix 6 I am coming out at a 50mm2 cable for 100 amps over 80 meters. This drops 6 volts over the run. [in the calculation I am using a soil resistivity of 1.2 as the ground is wet clay even in summer as there is a lot of groundwater, giving a rating factor of 1.4 for direct buried SWA]. This obviously is pretty close to the 3% limit for total voltage drop for any lighting circuits.
I am planning on protecting the SWA with a 100amp cartridge fused switch. The consumer unit would be down in the house which will have a pretty standard install.
Questions I Had (Any help/advice appreciated)
- What are people's thoughts on using 50mm2 or upping to 70mm2 to give more wiggle room on the voltage drop on the end of any lighting circuits (that aren't installed yet)? 70mm2 seems like an enormous cable given that the DNO would deliver it in 50mm2.
- Is it allowed to lower the amps in the voltage drop calculation because 1 house is very unlikely to ever pull 100 amps?
- Any issues with running in 2 x 25mm2 instead of a 50mm2 or 2 x 35mm2 rather than a 70mm2 (as both are easier to handle/terminate)
- Any other regs that would prevent the service cut from being so far from the installation?
Thanks
A.