Currently reading:
Cables In Parallel, Max Load?

Discuss Cables In Parallel, Max Load? in the UK Electrical Forum area at ElectriciansForums.net

bogney

-
Reaction score
1
Hi

Just wondering if someone could help me out with this one

Basically I'd like to know what's the maximum load (single phase) a 4 core 6mm SWA could deliver if cores were connected in parallel

SWA in buried under ground and the length is three hundred meters

The cable used to supply a 3 phase pump on a farm many years ago. The farmer would like to renovate pump house, and yep you guess it, want power down there.

Used a cat scanner to find and determine length.

Any help would on this would be much appreciated

Best regards

Dave
 
You need to ensure the safety of the two cables, in general the regs advise adding the CCC of each core.
In practise the CCC may be slightly greater but this is not accounted for in the wiring regulations.
Have a look at 433.4 and 434.4.
 
Shoot me down if I am barking up the wrong tree, I get conductors in parallel but what columns in Table 4D4A or 4E4A are you using to determine the current carrying capacity of the cable. Column 6 refers to a single phase load in a 2 core cable, however you have a single phase load in a 4 core cable so does this equate to Column 7 which is a 3 or 4 core cable on a three phase load. My view is Column 7 due to the quantity of conductor and not the fact it is single or three phase.
 
Your CCC would be 92A and your pump house perhaps a maximum of 50A so that would leave you 40A to divide among the caravans.
However your volt drop will be well beyond limits at that loading, especially as you want to extend further for the caravans.
I have just checked and I think you would need to keep your current below about 6A to keep within 6.9V (3%) drop over 300m with a 12mm² cable!.:):rowboat:
 
Your CCC would be 92A and your pump house perhaps a maximum of 50A so that would leave you 40A to divide among the caravans.
However your volt drop will be well beyond limits at that loading, especially as you want to extend further for the caravans.
I have just checked and I think you would need to keep your current below about 6A to keep within 6.9V (3%) drop over 300m with a 12mm² cable!.:):rowboat:
I assume you are doubling Column 6 from Table 4D4A to get 92A, problem is it ain't a 2 core cable?
 
I assume you are doubling Column 6 from Table 4D4A to get 92A, problem is it ain't a 2 core cable?
Yes I was doubling the tabulated CCC as recommended when using cables in parallel, however the regulations are thinking of two separate two core cables suitably arranged to ensure equal current sharing, which may well not be the case here, I agree.
However this is moot since the VD is something in the region of 50V!
 
Yes I was doubling the tabulated CCC as recommended when using cables in parallel, however the regulations are thinking of two separate two core cables suitably arranged to ensure equal current sharing, which may well not be the case here, I agree.
However this is moot since the VD is something in the region of 50V!
Not calculated the volt drop but under maximum loading I don't doubt it will exceed requirements.
 
OP: Email the concerns you have to the customer. That was you have proof that you have warned him about all the things. Just to CYA.
 
My view that cable if PVC insulated will be rated at 76A, if XLPE then 88A.

This is such a common mistake I see, you may well know this so it could just be for the benefit of others.

XLPE only has a higher current rating if everything it's connected to is also rated to operate at 90 deg C. If it isn't it's CCC is reduced to that of a PVC cable.
 
This is such a common mistake I see, you may well know this so it could just be for the benefit of others.

XLPE only has a higher current rating if everything it's connected to is also rated to operate at 90 deg C. If it isn't it's CCC is reduced to that of a PVC cable.

Reg 512.1.5 (Page 117) for reference to whoever wants to look it up.
 
This is such a common mistake I see, you may well know this so it could just be for the benefit of others.

XLPE only has a higher current rating if everything it's connected to is also rated to operate at 90 deg C. If it isn't it's CCC is reduced to that of a PVC cable.
Yeah know this, that however is the maximum rating of the cable where conditions satisfy.
 
In this case it clearly doesn't matter one jot what the CCC is, because at 300m the voltage drop limits you to about 6-7A as per RB above and the OP's observations.

If it were on my own turf, I would look at some kind of fun scheme like launching two phases into the two paralleled cores and transforming down 400 to 230 at the far end, which would give you three times the current for the same drop (before correcting for transformer regulation and loss which would undo some of the benefit) With 600/1000V cable and a tranny each end one could theoretically get about 29A through it at 3% drop and deliver over 100A at 230V at the far end, however the cost of buying and installing the transformers and the lifetime cost of their loss would probably exceed the cost of relaying in suitably sized cable.
 

Reply to Cables In Parallel, Max Load? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top