Search the forum,

Discuss can a consumer unit switch be replaced by an RCD? in the DIY Electrical Advice area at ElectriciansForums.net

You won't get RCBOs for that board. Being cynical here but the amount of undisturbed dust on the conductors and mcb switch toggles did they actually do anything in the consumer unit. If you redact any personal info seeing the EICR could be interesting.

Fair point.
 
Hi
You won't get RCBOs for that board. Being cynical here but the amount of undisturbed dust on the conductors and mcb switch toggles did they actually do anything in the consumer unit. If you redact any personal info seeing the EICR could be interesting.
Hi, can you tell me why I won't get RCBO's, is the board too old?
BTW its an old photo, was shot during some maintainance years ago
Here is the EICR for your perusal
 

Attachments

  • EICR FAIL cert- REDACT.pdf
    778.5 KB · Views: 29
All the circuits are listed as unknown and multiple tests are just LIM but with no reasoning. They say they didn't access the service head but have identified the earthing system as TN- S.
 
All the circuits are listed as unknown and multiple tests are just LIM but with no reasoning. They say they didn't access the service head but have identified the earthing system as TN- S.
Sorry I don't know what that means, can you tell me?
Thanks
Alan
 
How long were they there for.
The earthing system can generally only be verified by accessing the service head, they say they didn't access it.
 
How long were they there for.
The earthing system can generally only be verified by accessing the service head, they say they didn't access it.
Probably 40 mins or so, I think they did go into the basement where the service head is, but I didnt follow them so I don't know what they did
 
Forty minutes is no where near enough time to carry out an EICR even a small flat which explains why so many tests were not carried out.
 
Did they quote for a new consumer unit?
this looks Lazy, guy turns up has a look around.
sees no rcd so therefore decides it is going to be marked unsatisfactory anyway.
therefore why bother to go to all the trouble of testing stuff.

pulls a couple of cables from consumer unit, and measures resistance because the 2 circuits in question are easy, decides the rest is not worth his time.

about as much professionalism and attention to detail as a Friday night Donner Kebab.

and what is an 80% visual inspection of a consumer unit? I had a quick look but couldn't be arsed to look at it in any detail!!?
 

Reply to can a consumer unit switch be replaced by an RCD? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, NAPIT report was carried out due to flood, all kitchen appliances, wall/light switches, fire/heaters etc need replacing. The electrician...
Replies
4
Views
961
Hi, Hoping someone can clarify for me. I've recently moved into a rental property, the landlord had new electric radiators installed and a new...
Replies
3
Views
598
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
1K
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi, I am due EICR test on my property which has 20 year old wiring. Last test on 2018 was fine with no issues. Just need to check if my consumer...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top