Currently reading:
UK Can someone help me wire a new light fitting into an old house with old wiring systems.

Discuss Can someone help me wire a new light fitting into an old house with old wiring systems. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I’m a junior electrician, fresh out of college. I did some minor electrical work for a friend buI tried to put up a new chandelier I came across:
  • Two Line wires (RED), going into one connector block
  • Two Neutrals (BLACK), separated into different connector blocks
- Two CPC wires, going into one connector block.
The chandelier has one line, one neutral and one earth.

I wired it up putting the neutral in one neutral block. When turned on the bulbs barely lit up.
When i switched the wire to the other neutral block it lit up greatly, however could not be turned off.
When i put both neutrals in one block, the light lit up, but tripped the fuse when I attempted to turn it off.
I know little about old domestic systems. Can someone please advise.
 
I’m a junior electrician, fresh out of college. I did some minor electrical work for a friend buI tried to put up a new chandelier I came across:
  • Two Line wires (RED), going into one connector block
  • Two Neutrals (BLACK), separated into different connector blocks
- Two CPC wires, going into one connector block.
The chandelier has one line, one neutral and one earth.

I wired it up putting the neutral in one neutral block. When turned on the bulbs barely lit up.
When i switched the wire to the other neutral block it lit up greatly, however could not be turned off.
When i put both neutrals in one block, the light lit up, but tripped the fuse when I attempted to turn it off.
I know little about old domestic systems. Can someone please advise.
Where do you live Mate?????
 
I’m a junior electrician, fresh out of college. I did some minor electrical work for a friend buI tried to put up a new chandelier I came across:
  • Two Line wires (RED), going into one connector block
  • Two Neutrals (BLACK), separated into different connector blocks
- Two CPC wires, going into one connector block.
The chandelier has one line, one neutral and one earth.

I wired it up putting the neutral in one neutral block. When turned on the bulbs barely lit up.
When i switched the wire to the other neutral block it lit up greatly, however could not be turned off.
When i put both neutrals in one block, the light lit up, but tripped the fuse when I attempted to turn it off.
I know little about old domestic systems. Can someone please advise.


It's a three plate wiring system, one of the red/black/cpc cables is the live feed, the other is the switch.

Both lives (reds) together, to nothing else, the earths (cpc) together to all metal that can be touched when in use, the one switch wire (black) to the live of the lamp fitting, and the other neutral (black) wire to the neutral of the light fitting.

This isn't old, this is still current practice, only the colours have changed.
 
Even if the switch wire isn't identified, the fact that you use both black (or now blue) to the lamp means it doesn't actually matter (unless it's an edison screw) - although it's clearly preferable to identify the actual live to the lamp fitting.
 
Even if the switch wire isn't identified, the fact that you use both black (or now blue) to the lamp means it doesn't actually matter (unless it's an edison screw) - although it's clearly preferable to identify the actual live to the lamp fitting.
Egggh, I’m full of sunday roast, but I still don’t follow you.
 
Egggh, I’m full of sunday roast, but I still don’t follow you.

Which bit the es?

It's because with the es lamp fitting, it does matter, the switched live (which could be a red wire from the switch - if twin red, the black wire from the switch - if standard t&e,
Or black with red sleeve if std t&e done correctly) must go to the centre pin on an es fitting as it's polarised - and a test requirement.

But with a standard bayonet fitting, it doesn't really matter whether the black neutral goes to either connection, as long as the other black switch wire goes to the other connection on the lamp as they are not polarised.

(read brown/blue for new colours red/black - just kept with the old colours as that's what the original question was in)
 
Which bit the es?

It's because with the es lamp fitting, it does matter, the switched live (which could be a red wire from the switch - if twin red, the black wire from the switch - if standard t&e,
Or black with red sleeve if std t&e done correctly) must go to the centre pin on an es fitting as it's polarised - and a test requirement.

But with a standard bayonet fitting, it doesn't really matter whether the black neutral goes to either connection, as long as the other black switch wire goes to the other connection on the lamp as they are not polarised.

(read brown/blue for new colours red/black - just kept with the old colours as that's what the original question was in)
Modern ES holders are not polarity biased.
 
I gave a disagree Julie because you seem to be saying that it doesn't matter whether the black [or blue] switched live is clearly marked or not. Ok it'll work at the end of a loop in system with only two cables at the light but elsewhere you'd have a 1 in 3 chance of it working or not. :)
 
I gave a disagree Julie because you seem to be saying that it doesn't matter whether the black [or blue] switched live is clearly marked or not. Ok it'll work at the end of a loop in system with only two cables at the light but elsewhere you'd have a 1 in 3 chance of it working or not. :)

Yes, but I was referring to the op's question, which is at the end of the loop.

In addition, although not applicable to this case, when I first learned, there were strict placements for each wire, on the first three it would be: neutral to drop wire, neutral from supply, neutral to next fitting; on the next three: live from supply, live to next fitting, switch live to switch, then on the last two: switch wire from switch, live to drop wire.

The actual marking of the switch wire wasn't commonplace as you could easily identify it from the strict connection placement, and the way that cable was identified during first fix, don't think it is so strict these days, and of course lost when you fit another type of luminaire - which just wasn't likely back then!
 

Reply to Can someone help me wire a new light fitting into an old house with old wiring systems. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top