Do you use capping?

  • Yes plastic

    Votes: 8 38.1%
  • Yes metal

    Votes: 2 9.5%
  • Yes earthed metal

    Votes: 0 0.0%
  • Not needed

    Votes: 11 52.4%

  • Total voters
    21
Reaction score
36
Do you use capping to protect your cables? I recently watched a YouTube video explaining why you should use capping to protect your cables. I personally don't think it's needed for the following reasons;

- it's not in the regs. Although there are things in the regs saying to protect the cable from environmental factors and mechanical protection, it never says to use it. You could make a case for the regs implying too use it but I think it would be a poor case.

- very little extra mechanical protection, if any!

- a lot more time consuming.

- It's more expensive. this can be a real factor for a lot of people. Not a lot of people have the money for a rewire and adding that extra cost could be the difference.

But on the hand it does have its benefits;

- easy to replace cables. If that leg has an issue it's much easier to replace that leg or repair it when the cable has been capped all the way to the box.

- metal capping has more mechanical protection.

- prevents plaster deteriating cables.

All things considered when the choice is mine I think I will put it as an option for the customer for a fee of course, listing the pros of having it.

I'm an apprentice. Should be qualified next year. I would really value your opinions on why I should or shouldn't use capping. I've worked for 3 sparks and neither one have used capping. So I've only ever really heard one side of the argument. Thanks in advance.
 
Reality is on a 3 bed standard rewire the cost of capping as in cost to buy capping would be 50 quid , so on a £10,000 rewire the cost of capping is neither here nor there

I always tube / cap cables in chases , always have and always will , not using capping would be like not using grommets
 
Reality is on a 3 bed standard rewire the cost of capping as in cost to buy capping would be 50 quid , so on a £10,000 rewire the cost of capping is neither here nor there

I always tube / cap cables in chases , always have and always will , not using capping would be like not using grommets
Okay so £50 isn't a whole lot tbh. Taking into account not using cable clips etc. Fair enough. But then there's the fact that it takes longer to fit that, than to clip the cables. You told me earlier it would take like an extra minute to fit that in a chase than clip cables.. is that exadurating on your part? Taking into account all different types of walls how they're all easier or harder to clip or fit the capping.

I strongly disagree about comparing it to not using grommets though I must say. Grommets are much more effective at preventing mechanical damage and that's a fact.
 
Okay so £50 isn't a whole lot tbh. Taking into account not using cable clips etc. Fair enough. But then there's the fact that it takes longer to fit that, than to clip the cables. You told me earlier it would take like an extra minute to fit that in a chase than clip cables.. is that exadurating on your part? Taking into account all different types of walls how they're all easier or harder to clip or fit the capping.

I strongly disagree about comparing it to not using grommets though I must say. Grommets are much more effective at preventing mechanical damage and that's a fact.
To 'me' not using some tube or capping would be 'like' not bothering to use a grommet
 
I don't want this to seem untoward, but reading a discussion among electricians on the relative merits of capping is like debating which type of rock is best for hunting deer with.

There are better ways of containing and protecting cables, now please excuse me while I take cover for the remainder of this debate 😁
 
Before you go... What are the other ways? Genuinely curious. Don't mean for this to be an argumentative discussion. Again I am only an apprentice and value everyone's opinion :)

I'm also an apprentice, albeit of the reasonably mature variety.

The relaitve merits of plastering clipped cables, capping and oval or round conduit have been discussed here before, and some compelling arguments have been put forward for each, but in NI all solid wall cable drops are enclosed in round conduit and bushed into boxes and it would be inconceiveable to do anything else.

While I accept there are valid reasons why people might choose not to do this, it protects from trowels and future proofs installations to a reasonable degree. It's also fairly inexpensive.
 
I have always used metal capping or plastic tube, the time it takes to fit nowadays why wouldn't you. With modern screws and building materials and allband/ allround most of the time you can screw straight into block ect where a clip would just pull out again. Even drilling if it's hard and self gripping screws takes no time to do + you can usually pull cables out again if the customer change their minds.
 
Capping is there to prevent damage by the plasterer, no other reason. Necessary back in the day when wet solid plastering was the norm, as it was likely the trowel would make contact with the cable. The risk of this happening is much lower with dot n dab, and with chases in existing plaster, so not needed so much now. My preferred plasterer asks me to omit it, as he says it causes problems for him.

Easy to replace cables? Sometimes possible, but by no means guaranteed.

Mechanical protection? Not really, see the note on P77 of the OSG that explains why not.

Plaster deteriorating cables? This is a new one to me, can you link to something to back that up? I believe that PVC cables are fine with plaster, and T+E is specifically mentioned in the OSG as being suitable for being embedded in plaster.

I still use it sometimes, as it can be easier/quicker than clipping on some walls, and also for customer expectations. If I'm plastering the chases myself, I don't usually bother.
 
We could use some nice black plastic flexi-con bushed to each box and taken up into the floor / ceiling void which would make pulling in new cables nice and easy for the next bloke
 
We could use some nice black plastic flexi-con bushed to each box and taken up into the floor / ceiling void which would make pulling in new cables nice and easy for the next bloke

Or rigid conduit and avoid all the snagging that comes with cheap flexible conduit.

Cross the Irish Sea and you'll find this in all homes built during the last couple of decades - prior to that it was oval conduit squeezed into knockouts, but always extending into ceiling voids.
 
Capping is there to prevent damage by the plasterer, no other reason. Necessary back in the day when wet solid plastering was the norm, as it was likely the trowel would make contact with the cable. The risk of this happening is much lower with dot n dab, and with chases in existing plaster, so not needed so much now. My preferred plasterer asks me to omit it, as he says it causes problems for him.

Easy to replace cables? Sometimes possible, but by no means guaranteed.

Mechanical protection? Not really, see the note on P77 of the OSG that explains why not.

Plaster deteriorating cables? This is a new one to me, can you link to something to back that up? I believe that PVC cables are fine with plaster, and T+E is specifically mentioned in the OSG as being suitable for being embedded in plaster.

I still use it sometimes, as it can be easier/quicker than clipping on some walls, and also for customer expectations. If I'm plastering the chases myself, I don't usually bother.
This is why I have been taught to chase in deep enough so the trowel doesn't hit. Use the full length of the grinder.

Yes it is easier to replace the cables this way MOST of the time if done correctly. That is with oval conduit though. I should've been more specific.

Mechanical protection is provided with metal conduit. Again that's me not being specific, I assumed you'd pick up what I meant.

Yeah the plaster deteriating was something I literally learned quite recently. Take a look at guidance note 1 - 4.7 materials likely to cause such attacks include:
Plaster coats containing corrosive Salts: lime, cement and plaster.
Some examples of this
Placticisers migrate to ploystyrene from thermoplastic and also other types of plaster (see 7.5 also)

That's fair enough. I have never done it but I've been doing this for 3-4 years only and worked with 3 separate sparks whove never done it. I would be curious to see if it really is quicker because most people I speak to on this tell me that it takes a lot longer.

Thanks for taking the time to create a detailed comment.
 
This is why I have been taught to chase in deep enough so the trowel doesn't hit. Use the full length of the grinder.

Yes it is easier to replace the cables this way MOST of the time if done correctly. That is with oval conduit though. I should've been more specific.

If already chasing deep enough, I'd go the few extra pence on round pvc conduit and female bushes. Much easier to get cables through.
 
This is why I have been taught to chase in deep enough so the trowel doesn't hit. Use the full length of the grinder.

Yes it is easier to replace the cables this way MOST of the time if done correctly. That is with oval conduit though. I should've been more specific.

Mechanical protection is provided with metal conduit. Again that's me not being specific, I assumed you'd pick up what I meant.

Yeah the plaster deteriating was something I literally learned quite recently. Take a look at guidance note 1 - 4.7 materials likely to cause such attacks include:
Plaster coats containing corrosive Salts: lime, cement and plaster.
Some examples of this
Placticisers migrate to ploystyrene from thermoplastic and also other types of plaster (see 7.5 also)

That's fair enough. I have never done it but I've been doing this for 3-4 years only and worked with 3 separate sparks whove never done it. I would be curious to see if it really is quicker because most people I speak to on this tell me that it takes a lot longer.

Thanks for taking the time to create a detailed comment.
Ah, I see. When people say capping, I always think of the metal or plastic stuff that you fix over the cables, rather than oval/tube stuff that you thread the cables through (which I call conduit).

I shall have to buy a copy of guidance note 1 then, but it is the first time I have heard of problems with plaster on cables, and I have never come across any obvious damage to cables embedded direct. There is a passage in the OSG app. C warning about possible corrosion by plaster, lime, cement etc, but it is concerned with metal sheaths, conduit, armour and so on, rather than plastic cables.

Just a though - it couldn't be a typo in that text could it? If the word 'plaster' was replaced with 'plastic' the sentence would make more sense.
 
I don't think modern Plaster is as harsh on cables. The older lime Plaster and the likes was more of an issue. (Don't quote me on this) But still I would put some containment round it!
 
Ah, I see. When people say capping, I always think of the metal or plastic stuff that you fix over the cables, rather than oval/tube stuff that you thread the cables through (which I call conduit).

I shall have to buy a copy of guidance note 1 then, but it is the first time I have heard of problems with plaster on cables, and I have never come across any obvious damage to cables embedded direct. There is a passage in the OSG app. C warning about possible corrosion by plaster, lime, cement etc, but it is concerned with metal sheaths, conduit, armour and so on, rather than plastic cables.

Just a though - it couldn't be a typo in that text could it? If the word 'plaster' was replaced with 'plastic' the sentence would make more sense.

Agree - I suspect a typo there.
 

Reply to Capping or no capping? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top