Currently reading:
Changing fluorescent tube fittings to pendant.

Discuss Changing fluorescent tube fittings to pendant. in the UK Electrical Forum area at ElectriciansForums.net

J

janderson

light1.jpglight2.jpg

Hi,

I have removed 2 strip light fittings from the attic ceiling and would be most grateful if anyone could give some advice as to wiring some pendant fittings. The single wire seems straight forward but am not sure what to do with the double wires.

Many thanks
 
View attachment 26763View attachment 26764

Hi,

I have removed 2 strip light fittings from the attic ceiling and would be most grateful if anyone could give some advice as to wiring some pendant fittings. The single wire seems straight forward but am not sure what to do with the double wires.

Many thanks

Have a look at the note you made of the connections in the fluorescent light before you took it down.......you did make a note of the connections didnt you?......Oh,that was silly wasnt it?
 
Do you have a multi meter with a continuity buzz on it? If so you'll be able to find out which is the switched live without any danger. Then connect up as normal.
Sorry, thought you were a DIYer.
 
Did both lights come on together, fed by one switch? Could be T&E feed into one, then fed out to the other. In parallel like or summat eh? :) Daz
 
What wiring do you have at the switch?

If the fittings are switch fed then I would expect DPG has it right, each conductor would then be: red - switch line, black - neutral, green and yellow (once you have sleeved it).
If it is not switch fed then there must be a JB about somewhere as you do not have enough cables.
 
View attachment 26763View attachment 26764

Hi,

I have removed 2 strip light fittings from the attic ceiling and would be most grateful if anyone could give some advice as to wiring some pendant fittings. The single wire seems straight forward but am not sure what to do with the double wires.

Many thanks

Was it just 2 x fluos in loft or are there others off same switch? put up info that you took earlier when removing fittings
 
Just the 2 fluos in the loft.

Basically, the first set of wires (live, earth and neutral) went into a 3 way connector strip on the first unit. With the second unit the wires were doubled up. Two live, two earth and two neutral each going into each connector.
 
At a guess it sounds like non of the black cores we can see are switched lives so it should be straight forward. At the pendants, earth(s) into the earth terminal (remember to sleeve), the black(s) into the neutral terminal block (same block as the blue core from the pendant) and the red(s) into the same terminal block as the brown from the pendant flex (probably marked Live or switched live).

I am assuming a few things here ofcourse.
 
Agree Trev, test gear and the knowledge to use it would be the only sure way. Just picked up on the fact that all conductors of the flouri's went into that flouri's choc block......... didnt sound like there were any rogue choc blocks in there for a 'loop'. With lashed up house electrics though i share the sentiment........could be anything!
 
Heres a simple answer for you

Screw pendants up, put the two reds together in far left terminal of pendant, put two blacks together in far right terminal and the earths together in the bottom, repeat with the other pendant

Flick the breaker back on
 

Reply to Changing fluorescent tube fittings to pendant. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock