- Reaction score
- 2,046
Why must it?Must be 10mm on a 40a mcb... with the cooker switch rated at 45amps... my personal choice
Discuss Cooker supply 12kw correct cable size in the UK Electrical Forum area at ElectriciansForums.net
Why must it?Must be 10mm on a 40a mcb... with the cooker switch rated at 45amps... my personal choice
All that just to heat up a tin of baked beans
I meant from the outlet to the actual cooker, rather than from the OCPD to the isolator/outlet
I can’t recall seeing a domestic cooker/oven being able to take 10mm in its terminals
well if 6mm goes up to a total of 14/15kw and his is 17.7kw next cable up is 10mm and that’s a 40a breaker and obviously double cooker switch is rated at 45amps, might aswell do 10mm from the load to cooker aswell. My personal choice.Why must it?
True, but you charge the customer the extra money for the bigger size cable and it’s no real difference running it in. Even though it comes out at 30a I’d say you were pushing the boundaries. Nothing wrong with what your saying, just rather chuck a 10mm in. If I would of known my customer was putting in 12kw cooker (hense my original post) I would of put a 10mm in.... peace of mind I guessIf you use diversity then 17.7kw cooker comes out around 30A so in general 6mm2 is going to be fine imo.
Come installation day,engineertick box muppet commented old connection was wrong, and he had to check I had a 10mm 40amp supply for the new one. He also used a bit of 10mm tw&e from cooker outlet to oven.
corrected that 4U.
I've been meaning to clamp the thing on start up, just to see how many amps its pulling and for how long.
Well really bored and run out of View attachment 39827 So decided to clamp our 8.6kW cooker. Now meter's bit of a cheapie, and probably needs calibrating. But here's what I got on 244V; 39.4A.
By my calcu's should of been tad over 35A. Run it for a min or so, to allow things to settle.
Hasn’t took diversity into account... he’s just done 8600/240 which isn’t correct.... but mainly causes he’s ran out of beer
you might notice that i made no comment on your previous post so far.Okay so I couldn't be arse'd to stand out in the cold for your aresholes to allow the thermostats to cut in etc. Point I was trying to make was worst case situation, was max amps. Still be happy to connect to 32A 6mm supply. Jesus opps Holy Mary, cripes just be a bit more little horizontal you lot, its Xmas
Now that is dumb.Is it not obvious? He's run out of beer.
Okay so I couldn't be arse'd to stand out in the cold for your aresholes to allow the thermostats to cut in etc. Point I was trying to make was worst case situation, was max amps. Still be happy to connect to 32A 6mm supply. Jesus opps Holy Mary, cripes just be a bit more little horizontal you lot, its Xmas
Reply to Cooker supply 12kw correct cable size in the UK Electrical Forum area at ElectriciansForums.net