linuxthefish

-
DIY
Reaction score
4
Hi, I only have one socket to work with and adding others is not an option. Can I safely use an 1 socket 10 meter extension lead, with a 8 socket extension on the end? On the 8 socket extension i have a 6 socket extension lead (with another 1 socket extension) and and a 4 socket extension load. How many extension leads can I add before the 30mA RCD trips? Overloading should not be a problem, I have a 10A fuse in the 8 socket extension.

WALL SOCKET > 10 meter 1 socket extension lead > 8 socket extension > 4 socket extension + 6 socket extension cable (with 1 socket extension attached).

All that's plugged in is IT stuff, few laptops, audio amplifier, projector, fan, 2 40w lights, 3 monitors and a toaster sometimes.
 
Do you have access to a main switch to isolate in the event of an emergency ?

If the DNO fuse counts, then yes.

I get the impression the OP doesn't want to listen so I'm unsure why he asked in the first place TBH.

I'm more concerned about having the RCD trip or whatever, than overloading the 10A fuse in the socket. The cable near the plug has been shortened for anyone who is concerned, so it's not looped anymore :D
 
The RCD will trip if there is high earth leakage but if you are not concerned about over load then I am concerned ! Overload causes fire !! every time you add an extra extension lead the resistance is getting higher due to the connection between plugs and sockets and the length of cable Resistance means more heat more heat means fire !!!
 
The RCD will trip if there is high earth leakage but if you are not concerned about over load then I am concerned ! Overload causes fire !! every time you add an extra extension lead the resistance is getting higher due to the connection between plugs and sockets and the length of cable Resistance means more heat more heat means fire !!!

Sorry I may be having a blond moment but assuming the lead that is plugged into the supply socket is fused appropriately for all cables in the daisy chain (eg 13A rated all of them) then how can there be an overload risk? (I am assuming all unwound fully)
To me the issues are:
Disconnection times under fault (increased Zs value)
Volt drop
A serious effing trip hazard lol
 

Reply to Daisy chaining extension cables? Current leaking to earth? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top