DIY 16mm2 IP65 Junction box problem

Discuss DIY 16mm2 IP65 Junction box problem in the UK Electrical Forum area at ElectriciansForums.net

Solar2020

DIY
Reaction score
7
DIY poster : Hello, I am trying to connect two 16mm2 wires together in an ip65 junction box, but the holes are not big enough for the both the wires to push into. I am looking for a junction box that can join two 16mm2 wires. I have tried googling , even ordered things I though would work, but did not...so i am now asking here. In context :

I have a home 1.2kw/24v Solar setup. The two wires I want to join , go from my 450ah Battery Bank to my 800w Victron Inverter, to the left in the photo below. I have included a photo of an ip65 junction box with two wires joining together to demonstrate what I mean.

Thank you in advance for your help
 

Attachments

  • DSC_0323-min.JPG
    90.8 KB · Views: 101
  • DSC_0322-min.JPG
    69.2 KB · Views: 98
Hi Lucien, Darkwood et al, thanks for the replies, it is all very helpful, I am learning a lot. I did not realise the sheer number of connectors that exist in the electrical world. I now understand the elevated risks of screws against clamps and the possibility of poor terminations. I have a lot to consider and watch out for.

I might buy a selection and judge each once they have arrived. I will purchase the additional end stops and clamps Darkwood, so thank you for providing the additional information

I might not be able to reply much more tonight as I am providing surf life saving sessions tonight here in not so sunny Cornwall, but will read any replies and reply back tomorrow

Thanks again for all the help
 
If it's just those two cables you're trying to connect and it's indoor then a Henley block would suffice: 5-Way SP 100A Service Connector Block 25mm² - https://www.NoLinkingToThis/p/5-way-sp-100a-service-connector-block-25mm/82608#product_additional_details_container
 

Reply to DIY 16mm2 IP65 Junction box problem in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock