Do I extend the PME outside to a Log Cabin style building??

Discuss Do I extend the PME outside to a Log Cabin style building?? in the Australia area at ElectriciansForums.net

M

MATTMOUSE

Please forgive me in asking this same question which normally results in an arguement......lol

I friend of mine needs to have a supply installed (a lighting circuit, a heater circuit and a socket circuit) in a SWISS style log cabin located about 2 metres away from their main home which has a PME system.
The BIG question, Can I used the PME to supply the cabin?...........I wish to use either a 6mm or 10mm 3-core swa for the supply cable, RCD protected of course.

Sorry for this post, just wanted a few thoughts on this particular installation.

A huge thanx for any thoughts guys!!
 
You`v got a reliable earthing arrangement with PME....why the hell would you go back to an old fashioned system (TT)? Admittedly it has its place: building sites, Moorings etc but for a perminent fixed install....not if theres TN-C-S available.....keeps cropping up on here this one..........

tt is still common,out in the sticks..
 
A huge thank you for the replies guys!!...........at our depot, this topic always ends up in heated debates between the work force........lol
As for the cabin there will be no services or ext' metal parts to the structure and it will be placed on a concrete foundation raised from the ground for damp proofing.
So basically, the PME can only be extended outside a property if a minimum of a 10mm copper cable is used for the earthing, if 10mm is not being used ie: 6mm 3-core swa (3rd core as incomming earth) then its best to use the TT method............is this statment a good genric rule?
 
Not quite! The general rule is that the cpc on a circuit has to be a minimum 50% csa of the line conductors - hence if it were to be 6mm twin and earth the cpc would be 4mm, etc. So, if you're using 3 x 6mm cores as L1, Ln and R2 (so to speak) then you are more than adequately covered (assuming that the size of cable is appropriate to the load, of course). The 10mm cpc comes in when talking about Equipotential Bonding, as that is the minimum now suggested by regs.
 
Last edited:
Funny hoW exporting PME always gets alot of debate.

Here is another sticky by IQ

A good guide For 'exported PME' and

Its because people do not understand it - and quite reasonably so !

There is no publicly available information to give suitable calculations regarding typical DNO supply characteristics with regard to Circulating Neutral Network currents, Network currents under fault conditions, Probability of damage and danger occurring in domestic Installations environments, probability of damage and danger occurring in industrial, special locations, licensed premises. etc.,
Chapter 54 is filled with advice, tables and formulae regarding thermal constraints for S/C conditions.
But,
The only information given to us is table 54.8. Its given to us on a need to know basis and sparkies do not need to know!
You must always remember that there are a lot of insecure To**er* out there who once get hold of a little power will use it to protect their po*ition and *tuff everybody el*e.
 
I've watched one of the NICEIC learning videos where the gruesome twosome are doing a PIR, and the shorter one does the whole nine yards of working out the adiabatic in order to justify why a 6mm main earth is more than adequate in that situation. Talk about muddying the water!!
 
Thanx "Rockingit"..............So if theres no ext' metal parts that need "Bonding" in the cabin, then there's no need for the 10mm Equi bonding conductor.............could we not then rely on the 6mm swa 3rd core as the cpc supplying the cabin??............just a thought......lol
 
Thanx "Rockingit"..............So if theres no ext' metal parts that need "Bonding" in the cabin, then there's no need for the 10mm Equi bonding conductor.............could we not then rely on the 6mm swa 3rd core as the cpc supplying the cabin??............just a thought......lol

Yes, .....But!! If during installation the PVC sheath is damaged, then moisture ingress to the SWA can corrode the SWA in a relatively short time, ...time depending on the chemical make up of the soil it's buried in. I would always advise on using 3 core SWA, the cost difference is minimal, and your assured of a good CPC connection to earth when all connected correctly!!! It's a no brainer in my opinion!! ...lol!!
 
Respect to you guys for the info!!!.............is there a limit on how many seperate buildings (sheds, cabins etc) that you can use from one PME source?...........i heard that if lets say you have three sheds in your garden, you can only share or use the PME source from your main property for one shed and the other two must have a TT system.
Sorry to be a Parrot and repeat myself...........We can safely say that I can supply this cabin using the swa cpc and armouring (connected to the property PME MET) as the cabins incomming earth to feed various circuits (lighting and perhaps a small panel heater)
 
Respect to you guys for the info!!!.............is there a limit on how many seperate buildings (sheds, cabins etc) that you can use from one PME source?...........i heard that if lets say you have three sheds in your garden, you can only share or use the PME source from your main property for one shed and the other two must have a TT system.
Sorry to be a Parrot and repeat myself...........We can safely say that I can supply this cabin using the swa cpc and armouring (connected to the property PME MET) as the cabins incomming earth to feed various circuits (lighting and perhaps a small panel heater)

Where have you heard it?...I'd try reading 7671 instead.
 
Do it properly -make it a TT system
Run SUPPLY from the house distribution board to a new small distribution board in cabin with 2.5mm SWA
New, small distribution board in cabin will require a 30ma RCD for protection
Put a rod in the ground outside the cabin connecting to the dist' board with at least 16mm earth cable.
Put your feet up.
 
Do it properly -make it a TT system
Run SUPPLY from the house distribution board to a new small distribution board in cabin with 2.5mm SWA
New, small distribution board in cabin will require a 30ma RCD for protection
Put a rod in the ground outside the cabin connecting to the dist' board with at least 16mm earth cable.
Put your feet up.

...Another mythology disciple.
 

Reply to Do I extend the PME outside to a Log Cabin style building?? in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top