Currently reading:
Do I need over current protection?

Discuss Do I need over current protection? in the Electricians' Talk area at ElectriciansForums.net

if it is a fixed load, you could dispense with overload protection, but still need fault (short circuit) protection
 
I understand with a fixed load there is no chance of overload, but surely the short circuit protection will automatically give overload protection anyway even if it doesn’t need it.
Am I missing something?
no.you could have. say, a 2.5mm cable (27A CCC) protected by a 50A MCB giving fault protection, but the 50A MCB will not provide overload protection to the cable.
 
Upstream of the soft start, yes, downstream, no the soft start should be programmed to limit the overload current, if not the soft start instructions must give you the data you need.
Just remember if it's machinery BS7671 is irrelevant.
 
OP isn’t in UK? (Correct me if I’m wrong) So BS7671 is irrelevant anyway.
You're right, I saw the flag under his name and saw the little Union Jack and thought it was the whole flag, not just the small bit in the corner!
IEC 60364 still applies in AUS/NZ though it is a local interpretation like 7671, as would IEC 60204-1 which isn't so local.
 
Hi guys, i'm working on some project, do i still need over current protection if i'm using a soft starter and do I still need circuit breaker for that motor???
The soft start should have your overloads built in it you just have to read the manual and set to probably 115% X the full load of the motor and YES you have to have a circuit breaker for the soft start and motor
 
The soft start should have your overloads built in it you just have to read the manual and set to probably 115% X the full load of the motor and YES you have to have a circuit breaker for the soft start and motor

Why would you set to 115% of the FLC for a soft start?
Normally you set overloads to the FLC for DOL etc.
 
Why would you set to 115% of the FLC for a soft start?
Normally you set overloads to the FLC for DOL etc.
Not sure about the soft start, but they are usually sized ( 5hp 10hp ) so you have to put all the settings in. As
for the 115% is in article 430-250 of the NEC motors rated at 1.15 service factor is 125% Dave in the US we are taught to use the FLA on the motor and multiply it by 125%. All other motors multiply them by 115% the only information we use off the nameplate is the HP then you go to table 430-32(a1) of the NEC and find your hp and that’s where you get your amperage for that motor not the amperage on the
[automerge]1567306941[/automerge]
Not sure about the soft start, but they are usually sized ( 5hp 10hp ) so you have to put all the settings in. As
for the 115% is in article 430-250 of the NEC motors rated at 1.15 service factor is 125% Dave in the US we are taught to use the FLA on the motor and multiply it by 125%. All other motors multiply them by 115% the only information we use off the nameplate is the HP then you go to table 430-32(a1) of the NEC and find your hp and that’s where you get your amperage for that motor not the amperage on the nameplate
Dave I get what your saying on setting them in a soft start because it doesn’t have the in rush current a standard motor does. I’m not an expert on soft starts so I could have misquoted thinking about it
 
Last edited:
Not sure about the soft start, but they are usually sized ( 5hp 10hp ) so you have to put all the settings in. As
for the 115% is in article 430-250 of the NEC motors rated at 1.15 service factor is 125% Dave in the US we are taught to use the FLA on the motor and multiply it by 125%. All other motors multiply them by 115% the only information we use off the nameplate is the HP then you go to table 430-32(a1) of the NEC and find your hp and that’s where you get your amperage for that motor not the amperage on the
[automerge]1567306941[/automerge]

Dave I get what your saying on setting them in a soft start because it doesn’t have the in rush current a standard motor does. I’m not an expert on soft starts so I could have misquoted thinking about it

There is a common misconception in the UK that overloads need setting at more than the FLC, but normally they should be set at FLC as they are designed so that they cope with the inrush fir that setting.
 
Hi guys, sorry I haven't really send all the details about this, I've attached a photo of the diagram that the manual says, It says to put thermal overload relay? plus fuse upstream the soft starter? I'll be using this for a pump, I've also attached the photo of the details of the pump. Thanks much for helping and responding!

IMG_20190830_155840.jpg

IMG_20190902_113744.jpg
 
There is a common misconception in the UK that overloads need setting at more than the FLC, but normally they should be set at FLC as they are designed so that they cope with the inrush fir that setting.

It's a hangover from the old oil filled dashpots that were used for OL protection. These you had to have set at 100% FLC.

In regard to the OP, if the manufacturers state you need OL protection, then you need it. Maybe this model of SS doesn't have built in OL protection.
 
Fuse it (or use MCB) upstream of the starter to protect the equipment from short circuit, and use the overload to protect the motor from overload. You can use a combination MCCB for the complete protection provided it is of the correct type and is adjustable to the nominal motor current.

In the UK our regulations state that all motors above 0.37kW must have overload protection, I imagine your regulations will be similar.
 
Fuse it (or use MCB) upstream of the starter to protect the equipment from short circuit, and use the overload to protect the motor from overload. You can use a combination MCCB for the complete protection provided it is of the correct type and is adjustable to the nominal motor current.

In the UK our regulations state that all motors above 0.37kW must have overload protection, I imagine your regulations will be similar.
Yes, but, remember BS7671 is irrelevant when it comes to machiney.
110.2,xi
 

Reply to Do I need over current protection? in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock