- Reaction score
- 0
Hi guys, i'm working on some project, do i still need over current protection if i'm using a soft starter and do I still need circuit breaker for that motor???
Discuss Do I need over current protection? in the Electricians' Talk area at ElectriciansForums.net
I understand with a fixed load there is no chance of overload, but surely the short circuit protection will automatically give overload protection anyway even if it doesn’t need it.if it is a fixed load, you could dispense with overload protection, but still need fault (short circuit) protection
no.you could have. say, a 2.5mm cable (27A CCC) protected by a 50A MCB giving fault protection, but the 50A MCB will not provide overload protection to the cable.I understand with a fixed load there is no chance of overload, but surely the short circuit protection will automatically give overload protection anyway even if it doesn’t need it.
Am I missing something?
You're right, I saw the flag under his name and saw the little Union Jack and thought it was the whole flag, not just the small bit in the corner!OP isn’t in UK? (Correct me if I’m wrong) So BS7671 is irrelevant anyway.
The soft start should have your overloads built in it you just have to read the manual and set to probably 115% X the full load of the motor and YES you have to have a circuit breaker for the soft start and motorHi guys, i'm working on some project, do i still need over current protection if i'm using a soft starter and do I still need circuit breaker for that motor???
Sheff you left out the short circuit protectionOverload should be set to motor FLC. Job done.
Motor overloads are set to motor FLC in the IEC world, settings in the NEC world maybe different.Sheff you left out the short circuit protection
The soft start should have your overloads built in it you just have to read the manual and set to probably 115% X the full load of the motor and YES you have to have a circuit breaker for the soft start and motor
Not sure about the soft start, but they are usually sized ( 5hp 10hp ) so you have to put all the settings in. AsWhy would you set to 115% of the FLC for a soft start?
Normally you set overloads to the FLC for DOL etc.
Dave I get what your saying on setting them in a soft start because it doesn’t have the in rush current a standard motor does. I’m not an expert on soft starts so I could have misquoted thinking about itNot sure about the soft start, but they are usually sized ( 5hp 10hp ) so you have to put all the settings in. As
for the 115% is in article 430-250 of the NEC motors rated at 1.15 service factor is 125% Dave in the US we are taught to use the FLA on the motor and multiply it by 125%. All other motors multiply them by 115% the only information we use off the nameplate is the HP then you go to table 430-32(a1) of the NEC and find your hp and that’s where you get your amperage for that motor not the amperage on the nameplate
Not sure about the soft start, but they are usually sized ( 5hp 10hp ) so you have to put all the settings in. As
for the 115% is in article 430-250 of the NEC motors rated at 1.15 service factor is 125% Dave in the US we are taught to use the FLA on the motor and multiply it by 125%. All other motors multiply them by 115% the only information we use off the nameplate is the HP then you go to table 430-32(a1) of the NEC and find your hp and that’s where you get your amperage for that motor not the amperage on the
[automerge]1567306941[/automerge]
Dave I get what your saying on setting them in a soft start because it doesn’t have the in rush current a standard motor does. I’m not an expert on soft starts so I could have misquoted thinking about it
There is a common misconception in the UK that overloads need setting at more than the FLC, but normally they should be set at FLC as they are designed so that they cope with the inrush fir that setting.
Yes, but, remember BS7671 is irrelevant when it comes to machiney.Fuse it (or use MCB) upstream of the starter to protect the equipment from short circuit, and use the overload to protect the motor from overload. You can use a combination MCCB for the complete protection provided it is of the correct type and is adjustable to the nominal motor current.
In the UK our regulations state that all motors above 0.37kW must have overload protection, I imagine your regulations will be similar.
Reply to Do I need over current protection? in the Electricians' Talk area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.