Search the forum,

Discuss Do I need to use trunking ? in the UK Electrical Forum area at ElectriciansForums.net

Nice!!
Google says if the cables are not more than 50mm in the wall they should be mechanically protected and/or backed up by RCD. Since the cable is just behind the plasterboard and curvy it is RCD protected at the CU and we are going off a fused spur I’m going to assume plastic trunking just behind the plasterboard will be ok.
Trunking behind the plasterboard will be ok but the question is why? What is the point?
 
Doing some work in preparation for electrician to come in and wire it all up.

Going off your previous posts I don't believe your quote above is a truthful one.
What's the worst that could go wrong with wet naked bodies and electricity flowing just beneath your feet....but it's RCD protected so it will be fine...yeah course it will cos you have tested the RCDs and they are good to go.
Courtesy goes a long way in life. Hoodwinkery does not.
 
that "pinky" looking stuff is fireboard, you cannot make holes in it, so surface mounted conduit system is the general go to, but you could also frame it out infront of the fireboard to give a void to run cables.
 
Nice!!
Google says if the cables are not more than 50mm in the wall they should be mechanically protected and/or backed up by RCD. Since the cable is just behind the plasterboard and curvy it is RCD protected at the CU and we are going off a fused spur I’m going to assume plastic trunking just behind the plasterboard will be ok.

Plastic trunking is not acceptable as mechanical protection for buried cables. If mechanical protection is required it must resist penetration by screws, nails, drills etc or be of an earthed metallic type.
 
Why do you say each heating circuit should be on its own 16A circuit? We have not been given any information as to the actual load so how do you know what size circuit is required?

The manufacturers instructions for all the systems I've installed have required it and I take Appendix 15 (ii) which states "... not supplying comprehensive electric space heating or loads of a similar profile from the ring circuit" to preclude it as well.
 

Reply to Do I need to use trunking ? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock