In addition 'I think' Richard Burns has talked in a post (and drawn some good diagrams) about the 'opposite' RCD tripping. I.e a circuit on the right of the board making the RCD on the left trip. I can't quite get my head around this as there shouldn't be an imbalance. Anyway, that's digressing and I think you should start at the beginning with your N-E tests!
I hope I have not provided unclear information.
One key thing to remember is that (barring irregular voltage transients) if an RCD or RCBO trips then the fault must be on the circuit(s) that the RCD is protecting, the fault cannot be on a circuit not connected to the RCD.

However for a neutral earth fault present on a circuit protected by the RCD, a load on a circuit not protected by the RCD can allow diverted current to flow through the NE fault on the faulty circuit and trip that RCD, however the fault is on the circuit protected by the RCD, not on the circuit that appeared to cause the RCD trip.
RCD Trip due to other side loading.jpg
 
Last edited:

Reply to Dual RCD Problem in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top