Search the forum,

Discuss eicr code now 18th edition in the UK Electrical Forum area at ElectriciansForums.net

if it's compliant in all other respects, i'd not code it. however, under 18th. all luminaire circuits require RCD protection, so that would warrant a possible C3.
 
If it’s fit for purpose, no signs of thermal damage to the enclosure then why code it anything , Integrity of the enclosures IP ratings not included?
 
We code it a C3 as it is a non-conformance to BS7671:2018 but is not a safety issue.

A note is for something not covered by BS7671.

To not code it you are saying it is not a non-conformance which it clearly is.
 
653.2 The Report shall include the following:
- details of those parts of the installation that have been inspected and tested
- any limitations of the inspection and testing
- any damage, deterioration, defects or dangerous conditions
- any non-compliance with the requirements of BS 7671 which may give rise to danger.

Problem with code C3s, is there is no requirement to either comment or apply them.
 
If It’s a non compliance which doesn’t give rise to danger and fit for purpose then I don’t code these items, a bit like I don’t code red and black colours to the fixed wiring or a cpc identified with the colour green only.
 
Last edited:

Reply to eicr code now 18th edition in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock