Eicr no visible main bond to water services

Discuss Eicr no visible main bond to water services in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi all, it's been a while but been busy in work and setting up my fledgling company I have a question, have a eicr tomorrow on a ground floor ex council flat. Had a look round earlier and can't find the main equipotential bond to the water but it is visible at the met in the db, if the bonding is under 0.05 ohm near the stop clock, with the gas bond disconnected can I class this as a c3? The supply is tt BTW not that it should matter, any advice greatly appreciated
 
Yeah def needs mechanical protection, ze 88 ohms, job today ex council flat bonding everywhere except where it should be, gonna run a ten millimeter on the outside to external gas meter and complete at water incomer, who the hell installs these meters!, they haven't got the foggiest about bonding,, 6 mm clamped to upstairs flat the 10mm to the gas box, ffs mun
 