Search the forum,

Discuss Fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Yer paggas cut no ice this side of the Pennines.
We'll just overwhelm them with the riches and luxeries we enjoy over here!

Madchester
Aye? Well just see how much luxury ye got left when the Geordie hordes comes to rape your beer and drink your women.
You sir, are almost a mackem!
There you go, I said it.
He made me do it Fatha!
 
Last edited by a moderator:
Hello... Got a call from a. Customer saying when ever they plug in there 2kw heater it trips...

So One shal think the heater is faulty. I told them to unplug it and turn the rcd back on.

they rcd then restet... I thought over load may be a issue but she said she unplugged everything. She then plugged all the other items back in and it was fine.

But it she then got another heater and plunged that in put it in leval 2 and pop trips again.

Not been there yet.

Any by thing I should be looking out for when I arrive this week. Not seen this before ever. May be the fault current is to high? Maybe a slight short not big enough to trip the rcd but once the heater is on takes it over 30ma???

It maybe an alien inside the socket recharging their battery.

Rule one for fault finding:

Go and test the bloody job and don’t try to pre-empt the fault before hand!
The galling thing is you will charge the customer for the time you blunder about guessing what it may be.

Yet another Electrical Trainee wanting the job done for him.
 
These Mackems, they're not like Scousers are they?

Forgive me Fatha's Son!

By god! The Mancunian isn’t going to side with the Mackems is he? It’s OK to keep the Scousers out but there are limits when it comes to alliances.

Archy, just don’t side with the White Rose louts.
 
By god! The Mancunian isn’t going to side with the Mackems is he? It’s OK to keep the Scousers out but there are limits when it comes to alliances.

Archy, just don’t side with the White Rose louts.


OI! thought you were a mate. lol.
 

Hello... Got a call from a. Customer saying when ever they plug in there 2kw heater it trips...

So One shal think the heater is faulty. I told them to unplug it and turn the rcd back on.

they rcd then restet... I thought over load may be a issue but she said she unplugged everything. She then plugged all the other items back in and it was fine.

But it she then got another heater and plunged that in put it in leval 2 and pop trips again.

Not been there yet.

Any by thing I should be looking out for when I arrive this week. Not seen this before ever. May be the fault current is to high? Maybe a slight short not big enough to trip the rcd but once the heater is on takes it over 30ma???

Well there can't be many people nowadays that have a second 2kw heater available to use. It may well be that she has got them all over the house for all you know. When she says she's unplugged everything it may just have been in the room. It's pointless second guessing before you get there, so I would say this is a pointless question by yourself at the moment. Maybe if you have a look/test and are stumped.
 
Just recently I have had a few faulty RCBOs (load related), mostly the BG brand , would it be possible to plug this appliance into another circuit , just to eliminate that,
 

Reply to Fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
516
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
642
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
880
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock