Search the forum,

Discuss FCUs - Electricity needed for 2 Digital showers in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
i have recently had one bathroom redone. A spur was taken from a plug in the airing cupboard and put into a switched FCU with a 3 amp fuse as per Mira digital installation.

The second bathroom is now being done with another same digital shower next door to the other one.

I am assuming I cannot connect the two digital showers to this one 3 amp FCU?

Can I change the switched 3amp to an unswitched 13amp ?
Then connect two 3 amp switched fc units to the load side of the 13amp unswiched FCU.

My crude thinking is this then means each shower can have its 3amp fcu as per manufacturers instructions and the 13amp one will protect the cable and radial.

The consumer unit was also recently replaced with all seperate RCBOs

Is this allowed or any better suggestions please?
 
NO.... what you do is to fit another 3A FCU. this can be fed from the incoming side of the existing 3A FCU, or from elsewhere on the circuit.
 
as long as the 2nd FCU is fed from the incoming side of the first, it's just 2 x FCUs from the same point on the circuit If it were both FCUs were 13A, that could possibly cause an overload to the point on the circuit, but 2 x 3A is no problem. I assuming the circuit is a RFC, not a radial.
 
I guess adding another fused connection unit is really then a double spur off the ring, but as theyll both draw no more than 3A as said the risk of overload is non existant... Id be tempted to stick the second shower pump in the same fcu though tbh if it were my own house :D

Im sure your electrician will do it properly though and make sure its all safe and compliant... Let us know how he/she does it
 
I am assuming I cannot connect the two digital showers to this one 3 amp FCU?

You almost certainly could, particularly as you are unlikely to use both showers at the same time.

Or put a 5 amp fuse in the FCU.

Remember manufacturers instructions are guidance only and don't have to be religiously followed.
Think what happens when those showers are used in the majority of countries where FCUs are unavailable and non compliant. They are put straight onto a 16 amp circuit. The showers should be internally protected.
 
By rights you can’t have a spur from a spur but I don’t see a problem in this scenario as there’s no risk of overload during normal operation.

You could protect the whole spur by have a 13 amp unswitched FCU to protect the cable if you really wanted to abide by the regulations fully.

I would put the showers on double pole switched FCUs so you could isolate in case of fault in the future.

As these are supplying a special location you will more than likely need RCD protection and part P notification depending on your location.
 

Reply to FCUs - Electricity needed for 2 Digital showers in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock