Currently reading:
Fire Retardant Grommets

Discuss Fire Retardant Grommets in the Electrical Tools and Products area at ElectriciansForums.net

Marti

-
Arms
Reaction score
244
An interesting grommets question...hold the front page.
Wondered if anyone knew a supplier of the white fire retardant grommets normally used to seal a CCU at the point of cable entry?
Wylex and BG make pre-packed kits, somewhat over priced for what they are but they sort-of do the job. Unfortunately neither see fit to include 25mm; 20's and 32's being the standard fair and they are £7 - £10 a pack or about 10% of the price of a standard, dual RCD board and tails gland.
Apologies if this is a regular question. I did run search in the forum but without any clear success.
 
I've used them since 17th Ed. To me, non-combustible material includes the grommets. Granted the MCB, etc are plastic bodied but as any fire will go up, the FRG's make sense.
 
I've used them since 17th Ed. To me, non-combustible material includes the grommets. Granted the MCB, etc are plastic bodied but as any fire will go up, the FRG's make sense.

Fire retardent is not the same as non-combustible.
If you consider the grommets to be included in the requirment to be non-combustible then you would need steel grommets or a similar material.
 
I ran into exactly the same issue recently - since most boards have 25mm knockouts it's annoying that none of the kits seem to include any. I also could not find a single normal 25mm blind grommet in stock in any of the local wholesalers so had to wait to obtain one and return just to fill in a hole I didn't use in the end :mad:

I like the FRG as they are a lot easier to feed the cables through than a 25mm blind rubber grommet which usually has to be cut first.

Wiska do make them in 25mm, but not sure if anywhere does them separate - Their version of the BG/Wylex kit does include 3x25mm, Here or here for future reference

Wiska also seem to do a new type, with some strain relief built in, though I'm not sure how well they work for T&E
 
I believe the correct terminology is flame retardant not fire retardant, there is a difference.
 
They are not fire retardant.

What is the difference? as suppliers seem to interchange the terminology.
[automerge]1598133238[/automerge]

 
Last edited:
Suppliers have little or no technical knowledge. Strictly speaking it is fire resistant or flame retardant. Resistant meaning it is inherently resistant to catching fire as opposed to retardant whereby it has been chemically altered to self extinguish. Rubber as a compound will combust however if it is chemically altered it can self extinguish this is known as flame retardant.
 
Generally flame retardent is used to describe an item/product which has been treated or chemically altered so that it resists catching fire or is self extinguishing.

Generally a fire retardent is a substance which is used to slow down a fire, or fight a fire. The foam in a foam fire extinguisher is a fire retardent.
 
Generally flame retardent is used to describe an item/product which has been treated or chemically altered so that it resists catching fire or is self extinguishing.

Generally a fire retardent is a substance which is used to slow down a fire, or fight a fire. The foam in a foam fire extinguisher is a fire retardent.

Looks like the CEF ones are better value then :) !
 
Please specify the reg that you believe needs complying with.
421.1.201 that’s the one
[automerge]1598139945[/automerge]
Please specify the reg that you believe needs complying with.
I’ll be honest here, reason why I know this is because I got picked up on it by inspector A year ago when I used open grommets on consumer up tight to ceiling without proper fire sealing it and making sure it’s an enclosed chamber to prevent the escape of fire. He recommended the flame retardant grommets
 
The intent of Regulation 421.1.201 is considered to be, as far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames. Like so much else, it depends on your interpretation of the word "reasonably".
 
The intent of Regulation 421.1.201 is considered to be, as far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames. Like so much else, it depends on your interpretation of the word "reasonably".
I agree, just speaking from experience the inspector didn’t like open or blind grommets, I did though until then lol
 
421.1.201 that’s the one
[automerge]1598139945[/automerge]

I’ll be honest here, reason why I know this is because I got picked up on it by inspector A year ago when I used open grommets on consumer up tight to ceiling without proper fire sealing it and making sure it’s an enclosed chamber to prevent the escape of fire. He recommended the flame retardant grommets
As usual, The regs manage to make things more complicated by not being clear about their requirements and leaving it to people to find a way that most people thing complies.

I'd have thought open grommets wouldn't meet the IP rating for the top surface of a consumer unit in any case?

But all reg 421.1.201 really says is that consumer units should be manufactured from non-combustible material. It says nothing about any subsequent holes that you create in the thing during installation (it probably should imo). When using rear entry holes then there is not even an available flame retardant option that I'm aware of? Partly because they are not standard.

I've seen several of the Youtubers talk of filling the rear gaps with flame retardant sealant, but that doesn't seem to be a regulation, just an idea of 'good practise' that has grown up while people try to interpret what a reg means.

And since for CUs the only suitable example of non-combustible given is ferrous metal then if the reg applied to connections they'd also have to say that all grommets should be metal to be consistent, which isn't exactly going to work.

A lot of the meter tail glands now recommended are plastic anyway, and likely not flame retardant (Wiska do make one similar to their FR grommets having said that)

Personally I use the FR grommets because they are easy to force cables through (including post installation) and seal fairly well afterwards and although more expensive than blind grommets the cost is small compared to a consumer unit on a job.
 
Inspector of what? The building inspector?
[automerge]1598141883[/automerge]


That regulation says non-combustible, flame retardent is not non-combustible, these are different things.
Inspector from Council I done work for, it also states that cable entry points should be adequately sealed it’s a grey area but one which I unfortunately got made a mug out of. He had a couple of pages printed out in front of me and the main boss I can try and find them now and send the link IET I think it was from
[automerge]1598142923[/automerge]
Inspector from Council I done work for, it also states that cable entry points should be adequately sealed it’s a grey area but one which I unfortunately got made a mug out of. He had a couple of pages printed out in front of me and the main boss I can try and find them now and send the link IET I think it was from
1598142918023.png
 
Last edited:
Rather than grommets what about thsee ...

https://www.NoLinkingToThis/p/fireproof-gland-kit-red-20mm-10-pack/23277
 
Rather than grommets what about thsee ...

https://www.NoLinkingToThis/p/fireproof-gland-kit-red-20mm-10-pack/23277

I consider that to be false advertising.

Polyamide (nylon as it is often know as) is not fire proof.
It can be made self extinguishing with the right addatives

Just take a blow torch to one and see just how “fireproof” it really is.
 
From Hager’s manufacturers instructions
Read the cable entry part
Extract below

For rear cable access, the minimum number of knockout(s) shall be removed and a cable protector fitted; see illustration above.
Tests on hager consumer units have indicated that there is no specific need for external fire rated cable glands or intumescent sealing in addition to the guidance below, with respect to achieving a non-combustible enclosure. However this does not preclude the designer/installer from using fire rated cable glands or external intumescent sealing should they consider necessary. Internal intumescent pads shall not be used.
CA22217C-E1BF-454D-9BB8-9B83D935DECD.png
Also

cable access into the metal consumer unit must maintain the integrity of the non-combustable consumer unit so far as reasonably practicable. This can generally be achieved by the installer ensuring that cable access holes they make in the enclosure do not to leave gaps greater than:
· 1.0 mm for the horizontal top surface and
· 2.5 mm for all other surfaces of the enclosure that are accessible after installation.

So in conclusion, flame retardant or whatever you want to call it , grommets are not required but are not precluded, an inspector cannot fail or say it is unsatisfactory if you have not used them and quoting regulation 421.1.201 is pointless as that regulation does not specify such things.
A metal consumer unit is not a fire barrier, I mean for god sake there’s combustible mcb’s and devices installed In it.
 
Last edited:
From Hager’s manufacturers instructions
Read the cable entry part
Extract below

For rear cable access, the minimum number of knockout(s) shall be removed and a cable protector fitted; see illustration above.
Tests on hager consumer units have indicated that there is no specific need for external fire rated cable glands or intumescent sealing in addition to the guidance below, with respect to achieving a non-combustible enclosure. However this does not preclude the designer/installer from using fire rated cable glands or external intumescent sealing should they consider necessary. Internal intumescent pads shall not be used.
View attachment 60338
Also

cable access into the metal consumer unit must maintain the integrity of the non-combustable consumer unit so far as reasonably practicable. This can generally be achieved by the installer ensuring that cable access holes they make in the enclosure do not to leave gaps greater than:
· 1.0 mm for the horizontal top surface and
· 2.5 mm for all other surfaces of the enclosure that are accessible after installation.

So in conclusion, flame retardant or whatever you want to call it , grommets are not required but are not precluded, an inspector cannot fail or say it is unsatisfactory if you have not used them and quoting regulation 421.1.201 is pointless as that regulation does not specify such things.
A metal consumer unit is not a fire barrier, I mean for god sake there’s combustible mcb’s and devices installed In it.

Agree whole heartedly.

However BS7671is not always our only requirement to follow.

Often with big companies/councils there are adopted working practices which are the result of personal preference, which is fine if agreed to in advance.

Whats annoying is where you are not made aware of these foibles, don't do them and they try to make out its "best practice" or "in the regs".
 

Reply to Fire Retardant Grommets in the Electrical Tools and Products area at ElectriciansForums.net

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock