Currently reading:
UK First consumer unit change.

Discuss First consumer unit change. in the UK Electrical Forum area at ElectriciansForums.net

Raptor0014

Esteemed
Reaction score
1,261
Did my first consumer unit change yesterday.
A few dodgy things with the old board as I’m sure most will see.

Owner wanted bringing up to date with individual circuit RCD protection and surge protection.

So fitted a Fusebox 10 way RCBO board. Complete with surge protection.

Also removed the bell transformer that was being fed from a hole directly in the side of the CU and put the cooker cable into some conduit as the owner didn’t want it chasing in. I didn’t think it wise to leave it draping over the top of the CU like it was previously!

Any feedback is welcome as I’m always happy to learn from the more experienced amongst the forum.

Only thing I couldn’t seem to rectify is the slight leaning of the RCBOs/Main switch. No matter what I did as soon as I torqued everything up on the busbar it moved slightly.

One of the RCBO was a tad close on testing as you can see on the pic. But a pass is a pass and I tested that both at the board and at a socket (was on a Ring Final).

Anyhoo here are some pics.
C7DE9622-7934-44D3-8F86-0D824D4B6D89.jpeg
94E9EC2A-7FAC-4195-8250-311C72078E0E.jpeg
4EA7914E-843C-4007-BA3A-AB0A0B2EF814.jpeg
27DBD3AD-44C3-4FC9-AFF3-6ABEF5EFFA33.jpeg
9AFC177C-4103-4D5F-B608-2696271DF146.jpeg
90531D46-106B-4CB2-9BF9-400BEAEEC930.jpeg
30748230-A35C-4DA2-AFA9-288A284ACC4B.jpeg
0701D4FD-5696-4F6E-96A2-9230E1BE30CC.jpeg
23B84E49-3BB5-4948-94FA-47732EC978BE.jpeg
8869AA11-7326-4916-8F6B-C04A3B3149D5.jpeg
64189C8F-90DF-48C5-8C7B-D3DD3233FA8C.jpeg
 
It isn't. The cooker is on a 32a. It is in conduit for approx 1.2m then is clipped direct to the skirting board before chased into the wall to the socket (don't ask, I didn't install it! ?) Total length of the cable is approx 2.5m to the switch then approx 1.5m to the cooker terminal.

I worked out the load as it is a 7.43kw cooker.

So taking diversity into account the 6.0 & 32A is more than sufficient as it is 10A +30% of remainder (22.3a) = 16.69a + 5A for the plug socket on the switch = 21.69A.

6mm in conduit is rated to 38A & 34A once in the wall. So it's well within spec.

The 6.0 40A is supplying the garage and that is clipped direct.?
Apologies my error.
 
Very tidy job - well done. BTW looking at first photo of new board did you originally have it too close to the ceiling to get the cover on ;-) Most of us have similar at some point!

I have a Fusebox board sitting here - I'm fitting one tomorrow for the first time.
I'm impressed with it so far. The cover has screw catchers, the knock outs actually knock out, and it feels very solid. It's also a nice size to replace a 6 module rewireable Wylex if space is limited.

I very nearly did. Then luckily had a flash of wisdom.

The board is very nice and good quality. I was impressed with it myself. Just irked my CDO with the slight lean.
 
Very good first CU change @Raptor0014 ! Did you have a moment of worry when you saw hundreds of cables sticking out of the wall, with you the only one responsible for putting it all back together? ? I still remember that feeling from my first CU cjange.

Also very brave to put it online as every minor detail will be examined and criticised, still I guess that is what you want for learning purposes.

@westward does have a good point about the 6mm in conduit though, on a 40A breaker. I'm never too sure which reference method takes preference though when only a very short run is in the more strict reference method.

I will add reg 521.5.1 . I believe the main earth should enter through the same hole into the CU as the line and neutral tails, to negate possible electromagnetic effects. I stand to be corrected though. If I am correct then I will be chuffed that I spotted it before @westward10
 
Nice n neat good job ??, with regards the high readings I generally find fusebox pretty consistent with the trip times unless it’s a type A then they get abit close to maximum ?
 
[picky]B40 first on the busbar, not last.[/picky]

That was what I initially intended to do. But the way the cable run had been installed left it with no play and I didn't have time to take the covered walkway panels down, unclip it and see if there was enough play to move the RCBO nearer to the switch.

In reality I doubt the garage would ever pull anywhere near 40A. It's only got sockets and lights at the other end.
 
Can you give a valid reason for this.
used to be usual to put the highest loads closest to the main switch. the reasoning being that the larger load currents didn't have to travel further along the busbar. no logic behind it, it was realised about 30 yearsa go that the electricity did not leak out proportionaelyt to the length of the busbar and this pracice was stopped along with the old wives tale of "exporting the earth".
 
Very good first CU change @Raptor0014 !

Also very brave to put it online as every minor detail will be examined and criticised, still I guess that is what you want for learning purposes.

@westward does have a good point about the 6mm in conduit though, on a 40A breaker. I'm never too sure which reference method takes preference though when only a very short run is in the more strict reference method.

I will add reg 521.5.1 . I believe the main earth should enter through the same hole into the CU as the line and neutral tails, to negate possible electromagnetic effects. I stand to be corrected though.
See my other post, it's not in conduit.

Noted ref the earth.

And yes correct, this is why I posted to ensure I continuously improve myself. Nobody is perfect as they say.
 
Can you give a valid reason for this.

I'd always understood that highest loads should be placed closest to source of supply and accepted that without question. In the last few years I've read opinions that suggest there is no reason to do this and that it is better to populate a board by ensuring higher loads are separated to allow efficient dispersal of heat.

Not really in a position to comment, but the latter makes more sense and I'd be interested to read thoughts on the matter.
 
I'd always understood that highest loads should be placed closest to source of supply and accepted that without question. In the last few years I've read opinions that suggest there is no reason to do this and that it is better to populate a board by ensuring higher loads are separated to allow efficient dispersal of heat.

Not really in a position to comment, but the latter makes more sense and I'd be interested to read thoughts on the matter.
i agree. i never place 2 High load MCBs adjacent.
 
Type AC are being phased out it would seem. I only fit type A these days.
Stopped fitting them years ago. I don't personally see any merit in fitting Type AC anymore. For no (or minimal) extra cost with many brands it's a no brainer. That said, the FuseBox ones are substantially dearer than their Type AC, but thankfully I think they might be withdrawing the Type AC. There are neutral switching Type A compacts with FuseBox - so these are what I use when using that brand (although they are dearer).
 
The MEM add on RCD pods, MR30s don't like being tested at the board. They refuse to trip when tested. Apart from these, I always test RCDs at the board, preferably with no load connected.
But I also like to do a test at the other end of the circuit for good measure.
Yes correct the only way to test them at the board is to connect a short piece of cable to them . So general easy to test them at a socket on the circuit .
 
For a first CU change that really is very good - as others have said, it's much neater than a heck of a lot out there done by very experienced electricians. It's really encouraging to see that there are younger tradesmen out there with a really good attitude , well done.
Thank you

Wouldn’t say I was younger though. I’m 43 this year ?

I just chose to have a different career previously before having a complete change of direction.
It helps I suppose that I am OCD. ?
 

Reply to First consumer unit change. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top