Currently reading:
Flushing sockets in walls

Discuss Flushing sockets in walls in the Australia area at ElectriciansForums.net

0

067256

I want to flush about 3 or 4 sockets into the wall...existing cables are long enough thankfully.(sockets are currently surface mounted)
Do i need to make sure the circuit is rcd protected as i have an old wylex with push in breakers?
This is'nt classed as an addition or alteration????
 
as long as you are not modifying/extending the circuit. it's an accessory change so you don't need to bring the circuit up to current regs. however, i would check earthing and bonding as a matter of course, just to CYA.
 

Reply to Flushing sockets in walls in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock