I want to flush about 3 or 4 sockets into the wall...existing cables are long enough thankfully.(sockets are currently surface mounted)
Do i need to make sure the circuit is rcd protected as i have an old wylex with push in breakers?
This is'nt classed as an addition or alteration????
 
as long as you are not modifying/extending the circuit. it's an accessory change so you don't need to bring the circuit up to current regs. however, i would check earthing and bonding as a matter of course, just to CYA.
 
if they're surface at the moment, he'll need knock-out boxes anyway.
 

Reply to Flushing sockets in walls in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
571
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
322
An odd question granted but bear with me. I've got to extend a radial circuit in a community centre to fit a new hand dryer in the toilets, but I...
Replies
15
Views
3K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock