I take it Wilson that you are referring to Appendix 14 of BS7671, the diagram shows all scenarios for a RFC and indeed the requirements for installing spurs from the RFC.hello I've seen the page at the back of the regs book but nothing explains can you -
Have a spured socket off the ring using one cable and then put a fused spur after the spur and then feed additional sockets after the spir
What you could do however is swap the Spurred socket for a fused spur and then add as many sockets as you like,
hello I've seen the page at the back of the regs book but nothing explains can you -
Have a spured socket off the ring using one cable and then put a fused spur after the spur and then feed additional sockets after the spir
TTC I think the OP was wanting to spur off of a socket to another socket using a single 2.5, and then from that spurred socket to another fused spur to feed some more socketsThere is nothing to stop you having two spurs from the socket on the ring.
One spur to the additional socket, one spur to the FCU/
There is a physical problem of cramming 4 x 2.5 conductors into the back of the socket.
If I was you, I would do as Pete says above
Original socket to new spurred socket to FCU to feed more sockets. I'm getting a headache now. What you said above is how it should be done, now where are the headache pills?Ahh ok. Spur to FCU then on to additional sockets.
Correcta munda, mon ami, zat is what I believe Monsewer OP meant.
and you are never 39 and a quarter
Many would not agree that this is acceptable, as you are not supposed to concentrate loads at one point on the ring. Indeed, the informative appendix mentioned does not allow such an arrangement. However, as the appendix is informative it does not actually form part of the Wiring Regulations.There is nothing to stop you having two spurs from the socket on the ring.
Whilst I agree with Risteard that Appendix 14 is an informative Appendix, saying that it doesn't form part of BS 7671 "The Regulations" When you actually read APP14 it does quote several Regulation Number414.4Many would not agree that this is acceptable, as you are not supposed to concentrate loads at one point on the ring. Indeed, the informative appendix mentioned does not allow such an arrangement. However, as the appendix is informative it does not actually form part of the Wiring Regulations.
It's informative, it's not the Regulations.
Yes it may be in a book called 'Requirements for Electrical Installation', but that doesn't mean anything.
All it does, is inform you certain methods for complying with the Regulations (well not actually the Regulations, cos these are requirements, not Regulations).
So just to clarify, although appendix 15 is in the book we call the 'Regulations', it's not actually in the 'Regulations'.
It's part of the book which we call the 'Regulations', but it's not part of the 'Regulations'.
Hope that clears everything up.
So with than analogy, just because "GENISIS is in the Bible doesn't make it part of the Bible?Depends whether you look at the front, or on the spine.
Anyway, that's beside the point.
Just because something is in a book called the 'Wiring Regulations,' doesn't mean it's part of the Regulations.
Ok?
Confused.comYes, exactly.
Just because it's in the Regulations, doesn't mean it's in the Regulations.
Hope that clears that up.