Discuss Fused spur off ring main regulations in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Wilson12

-
Trainee
Reaction score
3
hello I've seen the page at the back of the regs book but nothing explains can you -
Have a spured socket off the ring using one cable and then put a fused spur after the spur and then feed additional sockets after the spir
 
hello I've seen the page at the back of the regs book but nothing explains can you -
Have a spured socket off the ring using one cable and then put a fused spur after the spur and then feed additional sockets after the spir
I take it Wilson that you are referring to Appendix 14 of BS7671, the diagram shows all scenarios for a RFC and indeed the requirements for installing spurs from the RFC.
Your question would be a no you can't spur a socket using a single cable, and then add a fused spur to supply more sockets. What you could do however is swap the Spurred socket for a fused spur and then add as many sockets as you like, what you are suggesting amounts to 2 spurs from the same point. Hope this helps.
 
Can you draw what you are asking. But it sounds like no, if I understand you correctly. Although saying that it hasn't stopped many others from doing so from what I see when attending various sites.
Aha manitas de plata has beat me to it.
 
There is nothing to stop you having two spurs from the socket on the ring.
One spur to the additional socket, one spur to the FCU/

There is a physical problem of cramming 4 x 2.5 conductors into the back of the socket.

If I was you, I would do as Pete says above
What you could do however is swap the Spurred socket for a fused spur and then add as many sockets as you like,
 
hello I've seen the page at the back of the regs book but nothing explains can you -
Have a spured socket off the ring using one cable and then put a fused spur after the spur and then feed additional sockets after the spir

If I read correctly then no you can't do what you suggest. Think about the maximum potential load on the first section of cable spurred from the ring.
 
There is nothing to stop you having two spurs from the socket on the ring.
One spur to the additional socket, one spur to the FCU/

There is a physical problem of cramming 4 x 2.5 conductors into the back of the socket.

If I was you, I would do as Pete says above
TTC I think the OP was wanting to spur off of a socket to another socket using a single 2.5, and then from that spurred socket to another fused spur to feed some more sockets
 
Ahh ok. Spur to FCU then on to additional sockets.
Original socket to new spurred socket to FCU to feed more sockets. I'm getting a headache now. What you said above is how it should be done, now where are the headache pills?
 
There is nothing to stop you having two spurs from the socket on the ring.
Many would not agree that this is acceptable, as you are not supposed to concentrate loads at one point on the ring. Indeed, the informative appendix mentioned does not allow such an arrangement. However, as the appendix is informative it does not actually form part of the Wiring Regulations.
 
Many would not agree that this is acceptable, as you are not supposed to concentrate loads at one point on the ring. Indeed, the informative appendix mentioned does not allow such an arrangement. However, as the appendix is informative it does not actually form part of the Wiring Regulations.
Whilst I agree with Risteard that Appendix 14 is an informative Appendix, saying that it doesn't form part of BS 7671 "The Regulations" When you actually read APP14 it does quote several Regulation Number414.4
and there are references to several chapters, and I quote 433.1.204 which need to be referenced in conjunction with Appendix 14, so I'm sorry to disagree Risteard, but I find it hard to agree with your statement, no disrespect intended.
 
It's informative, it's not the Regulations.
Yes it may be in a book called 'Requirements for Electrical Installation', but that doesn't mean anything.
All it does, is inform you certain methods for complying with the Regulations (well not actually the Regulations, cos these are requirements, not Regulations).
So just to clarify, although appendix 15 is in the book we call the 'Regulations', it's not actually in the 'Regulations'.
It's part of the book which we call the 'Regulations', but it's not part of the 'Regulations'.
Hope that clears everything up.
 
It's informative, it's not the Regulations.
Yes it may be in a book called 'Requirements for Electrical Installation', but that doesn't mean anything.
All it does, is inform you certain methods for complying with the Regulations (well not actually the Regulations, cos these are requirements, not Regulations).
So just to clarify, although appendix 15 is in the book we call the 'Regulations', it's not actually in the 'Regulations'.
It's part of the book which we call the 'Regulations', but it's not part of the 'Regulations'.
Hope that clears everything up.

The book called "IET wiring regulations" ? ;)
 
Depends whether you look at the front, or on the spine.
Anyway, that's beside the point.
Just because something is in a book called the 'Wiring Regulations,' doesn't mean it's part of the Regulations.
Ok?
 
Last edited by a moderator:

Reply to Fused spur off ring main regulations in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
689
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
699
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
240
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Replies
4
Views
575
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock