Grid voltage at the consumer unit of a house?

Discuss Grid voltage at the consumer unit of a house? in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
5
Hello,
We have installed equipment at a customer location, (or rather, an external electrical contractor installed it for us). The equipment is internet monitored by us…..and we are noticing that the Grid voltage is regularly falling to 225VAC. Our equipment disables at this low grid voltage.

We are trying to find out if the reason for the low grid voltage is because the wiring that the electrician used was too thin in gauge (too resistive). Then, the current flow through it would make the voltage at the equipment terminals be low, due to the resistive voltage drop.

So we want to find out what is the true grid voltage at the consumer unit of the house?
Can smart meters give a grid voltage measurement.?

Is there any safe way that we can get the customer to probe the grid voltage at his consumer unit?
 
Hello,
We have installed equipment at a customer location, (or rather, an external electrical contractor installed it for us). The equipment is internet monitored by us…..and we are noticing that the Grid voltage is regularly falling to 225VAC. Our equipment disables at this low grid voltage.

We are trying to find out if the reason for the low grid voltage is because the wiring that the electrician used was too thin in gauge (too resistive). Then, the current flow through it would make the voltage at the equipment terminals be low, due to the resistive voltage drop.

So we want to find out what is the true grid voltage at the consumer unit of the house?
Can smart meters give a grid voltage measurement.?

Is there any safe way that we can get the customer to probe the grid voltage at his consumer unit?
c
 
Contact the DNO
And you can expect them to do absolutely nothing, they may install a voltage recorder but if it is within the lower and upper limits then they will do nothing other than advise it is within limits
Which is exactly the response I got from ENWL when my voltage was fluctuating between 221v and 251v over a number days / weeks which I had recorded with my own PQA
 

Reply to Grid voltage at the consumer unit of a house? in the Electrical Appliances Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock