i understand the need, as I see it any circuit with a likelihood of more than 10 mA earth leakage should be subject to high integrity earthing.

This requirement can be achieved by many methods and I can see the sense in some.

Using RFCs instead of radials gives two paths so in the event of a break in the CPC it is still unlikely that the earth leakage will achieve mains potential. But why does it stipulate a 4mm CPC?

Is the use of 10mm simply a fudge so that distribution circuits can be classed as high integrity eathed?

Must admit to finding this confusing but interesting.
 
Are you reading the OSG section on high integrity earthing ? If so the referenced regs should help.
10mm is the minimum conductor size for an independent protective conductor ..... unless it's made of copper, then it's 4mm.

I think that's right. I'm up to my cerebral cortex in certificates right now so please do check.
 
I think it’s to do with the robustness of the conductor.
It’s worth pointing out that the 4mm would need to be mechanically protected if used for high integrity earthing say in a radial circuit
 
Then it would not be a single protective conductor so yes.
A single copper protective conductor having a CSA of not less than 4mm complying with regulations 543.2 and 543.3.
The protective conductor being enclosed to provide additional protection against mechanical damage
If not mechanically protected then the minimum CSA is 10mm
543.7.1.203 indent (ii)
 
Last edited by a moderator:
If I'm reading OSG 7.5.3 correctly, the good old RFC 2.5/1.5 can be re-configured to be high integrity (?).
It can but if you wanted to use a radial circuit then as long as you have mechanical protection throughout its length, 4mm can be used so there’s 2 earth connections at each point including any junction boxes, Spurs and at the DB with the cpc installed as a ring configuration format.
 
I think it’s to do with the robustness of the conductor.
It’s worth pointing out that the 4mm would need to be mechanically protected if used for high integrity earthing say in a radial circuit[/
4mm is the minimum size used for bonding without mechanical protection 2.5 and smaller are not strong enough.
 
Yeah, that Marv....dunno what we're gonna do with him.

I deleted a few feisty posts before the last reply I made in this thread so maybe that caused confusion.
 

Reply to High integrity earthing. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock