Search the forum,

Discuss Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net

echase quote:


E.ON calculates the higher tariff on a daily basis ie in my case 900kWh/year divided by 365 (approx 2.5kWh) charged at the higher rate for each day first plus the remaining power used that same day at the lower rate.


Unless you have a smart meter I assume they don’t know what your daily usage is. So every time they do “know” (quarterly when readings taken or estimated) they will make your calculation and average it over the quarter. So assuming when averaged your daily usage is always >>2.5kWh it means you in reality pay the lower rate for any extra gas you use for water heating. It will only be the higher tariff if you use very little gas in summer, e.g. don’t have gas cooking, so bringing your base load usage without water and house heating below 2.5kWh.

To remind you all the original question was about whether using one unit of gas for water heating was priced at the higher or lower tariff.
 
Unless you have a smart meter I assume they don’t know what your daily usage is. So every time they do “know” (quarterly when readings taken or estimated) they will make your calculation and average it over the quarter. So assuming when averaged your daily usage is always >>2.5kWh it means you in reality pay the lower rate for any extra gas you use for water heating. It will only be the higher tariff if you use very little gas in summer, e.g. don’t have gas cooking, so bringing your base load usage without water and house heating below 2.5kWh.

To remind you all the original question was about whether using one unit of gas for water heating was priced at the higher or lower tariff.

Sorry, maybe my explanation wasn't clear enough.
E.ON's higher rate tariff is 22.27p/kWh for the first 900kWh used in a year; thereafter the rate is reduced to the lower tariff of 10.13p/kWh used in the year.
This doesn't mean you pay at the higher rate until you have used the first 900kWh in the year up front.
They divide 900 by 365 days so each day you pay the higher rate on the first 900/365 (approx 2.5kWh) & then at the lower rate on the remainder of power used on that day.
So every customer pays the same for each days higher rate usage (assuming they use at least 2.5kWh), which, I assume replaces the old daily standing charge that no supplier seems to use any more.
This higher rate daily charge comes out at about £0.55 for the first 2.5kWh thereafter the charge depends on the extra days units used but charged at the lower rate.

The same method is used for charging for gas but with different higher & lower rates to electricity in my case 6.859p/kWh for the first 2,680 kWh used in a year then 2.98p/kWh for the remainder used in the same period
Hope this is a bit clearer?
 
I have read your web posting with interest - very detailed and scientific

Thank you.

1. As others have said 3kWh is very low for the heat absorption available - either you are starting with less than half a tank of hot water or a short immersion heater - as a typical 100 litres tank requires 9kWh to heat from 10 DegC;

Yes, I think we probably have a short immersion. I'll be checking that out when we get a warm day and the central heating stays off! I'm planning to check with an external heat sensor.

2. Your boiler efficiency may be 70% but this will be degraded by pipework losses and boiler cycling to a more typical 60% in the summer;

Agreed - and some folks believe even less. As it happens my old Camray is rated at 70%, but hopefully a newer condensing boiler at something like 93% efficient should come down to around 70% or better when taking pipes and other losses into account.

3. The orientation of your panels maybe a significant factor in output available so far as low winter sun will not be able to give much generation;

Yes, as I mention in the article, the panels are WSW which isn't terribly good. Also, it tends to be cloudy in the Vale of York. On the bright side, in the last month the panels offset 200kWh we would have pulled from the grid, but we did export 130kWh for our neighbours to use - if only there were some way to use that locally ;)

4. Your base load of 800W seems very high, 300W seems more typical - as with all good energy management you should go round turning off things on standby, etc.

Indeed, it is high. Overnight it's down to about 350W but sadly during the day we're in the house. To be honest we get good value from the power we're using and tend to leave large loads until the sun is shining. With two young children who like muddy puddles, plus two adults doing computer-based work at home I sometimes think we are lucky to come in at 800W!

Interesting to see how your calculations develop over the next few months as I reckon that 1.5kW differential is break-even with gas and a 4kW system should give significant savings over the summer with a 3kW heater.

Yes, you could be right. Although my web page says "oil", you could insert values for a gas based system into those text boxes and see what it says. I'm hoping to update it when I have more data - it could be enough to capture 'til the Summer solstice and then double everything up for a rough idea.

By the way, feel free to ask if there's some way of presenting the data that would help explain things you're interested in. Sadly the calculations included over 1million readings each for the house and solar over three months so even if I make my Javascript very fast, it'll stress your computer doing the detailed calculations.

If you have read all the posts on this thread you will be aware that I am marketing a simple SolarHeat controller which does not measure the differential but is cheap(ish) and can be configured to switch at 1.5kW or 2.5kW output. I recommend this type for summer use only.

Sounds like a good plan. Best of luck with your sales.
 
Hi echase and all,, I have one of these £32.00 gizmos,and yes it does do what it says, and works well"ish,,
as echase say's you are constantly wondering if it's set right, I have it on a1800w water boiler which boils in no time, then I have to alter it to run aNight storage radiator, which I rewired so as to put on one element or allthree 2500w, constantly watching the power generated, to see if I can switch onthe other elements, it's not ideal, if I set it to run one element 850w, thengo out and the sun shines I am wasting all that energy.
If you want to run 1KW all the time then I guess its fine.
Waiting for something more intelligent to come along

 
Hi - new to the forum - haven't (unlike some new joiners) spent the full 2 days reading all 39 pages, but I have browsed thro' quite a few, suitably impressed with what seems to have been happening here over the past 18 months. What started out as a simple question, and thoughts of switching in an extra 1kW heating element, seems to have evolved almost into an online multi-participant product development workshop, with some deep discussions and brilliant ideas emerging.

Like others we've just had solar PV installed and have now realised the desirability of using it to heat our water also - at present we have no gas, so water & space heating are all electric (storage heaters for the latter). From the forum discussions I'm persuaded that I need to look beyond the Parsons Switch plus 1kW element towards a fully responsive device that will track the generation and use all the surplus available using the existing 3kW immersion element.

If I understand correctly a couple of the regular posters - echase, pmcalli, and a couple of others - have fairly advanced product designs. Is there an FAQ listing these, or links to obtain more information ? I'd like to get something installed in the next month or so, so I can benefit from the increasing sunshine

Many thanks,


Walter
 
Hi echase and all,, I have one of these £32.00 gizmos,and yes it does do what it says, and works well"ish,,
as echase say's you are constantly wondering if it's set right,

A lot of people posting here are asking me if they can buy one of my ready built units. The best offer I can make is to say that they should be available from back end of this year, unless you also want a PV system, in which case you can buy a PV system with my unit now.

If you don’t want to build your own unit based on the designs offered here my recommendation would be to consider one of these £32 units (altough I have never had one in my hands) and use a less than 3kW load on it. That may recover much of its cost in the next year if you don’t mind constantly fiddling with it and worrying about the electricity you are “incorrectly” using/diverting. Then sell the £32 one on eBay and get one of mine which will pay for itself in much less time than your PV system will and needs no fiddling. That all assumes you have a >3kW PV system and do the installation yourself, otherwise the paybacks change.
 
Inspired by some of the folk on this thread (and elsewhere) I spent some winter evenings putting together a combination of Arduino, Crydom SSR, current and voltage sensor, LCD display etc. and now have the capability to monitor export v import with fully dynamic proportionate load control to match the immersion load to net export from solar PV and the rest of the house. So far so good, and I thought I'd finished the difficult bit! I have a 210L Tribune unvented direct cylinder and can hook this up to the bottom immersion unit, but that still means I'll need a grid top-up if I use lots of water in the evening. What I want to do to finish off my system is to install a second cylinder upstream of my existing cylinder as a pre-heat (which lots of others have mentioned). That way if the sun shines a lot - or shines a little over two days when I don't use much hot water - the pre-heat tank should get hotter than my existing one, so I shouldn't need any grid top up at all, and all surplus generation can be harvested until the pre-heat tank tops out at say 85 degrees. But Heatrae Sadia say installing a pre-heat tank between the reducing valve and their cold inlet is against Building Regs so can't be done. Most of the unvented pre-heat cylinders out there seem to be marketed for use only with combi boilers. Has anyone installed two unvented tanks in series in a way that works for Building Regs? The acceptable alternative is to install in parallel and rely on mixing/ diverter valves but that adds complexity/ cost/ more things to go wrong and lacks the simplicity of a pre-heat.
 
I would recommend reading all the posts. I've just finished making pmcalli's gadget, it does exactly what I want, excess P.V. Going to a 3kW immersion. I would PM him mate, he's extreamely helpfull. Good luck !!
 

Reply to Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
498
The unit only heats water using the programmed boost and when pressed in the 1 2 or Cont boost function. I have checked the off-peak time which...
Replies
7
Views
489
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
Hi All. Its been ages since I have been on here- Fortunately log in details stored on PC. I have just had a new boiler and 210 ltr unvented tank...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock