Search for tools and product advice,

Discuss Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net

echase, good to see you are still keen to get your product to market
any ideas on dates for this?
have you recieved your test sample and destroyed it yet?
we are sat on the fence with our R&D at the moment as your product sounds perfect but its all about timing, take care
 
echase, good to see you are still keen to get your product to market
any ideas on dates for this?
have you recieved your test sample and destroyed it yet?
we are sat on the fence with our R&D at the moment as your product sounds perfect but its all about timing, take care

Tried to send you a PM but your inbox is full.

Samples are too strong to break. Lots of them have passed all sorts of testing.
 
Last edited:
I have been looking at a unit to just that but it is SO expensive. I have 3.8 kw pv and would like to spill the excess to the immersion heater. Any chance of some info on how you are doing it?
Thanks

Hi,

I had the same requirements after getting a 2.8kW rent-a-roof scheme installed.

I have designed a circuit that will automatically use the excess power generated by your solar panels. It monitors the load and the generated solar power and uses the difference to control a 3kW dimmer.

I'm sharing my circuit and hopefully this will produce improvements to the circuit for all to use.

Details can be found at www.talkingsolar.co.uk
The website is still being developed (very slowly) so bear with me.

Cheers, Keith Walker
 
Last edited by a moderator:
Hi,

I had the same requirements after getting a 2.8kW rent-a-roof scheme installed.

I have designed a circuit that will automatically use the excess power generated by your solar panels. It monitors the load and the generated solar power and uses the difference to control a 3kW dimmer.

I'm sharing my circuit and hopefully this will produce improvements to the circuit for all to use.

Details can be found at www.talkingsolar.co.uk
The website is still being developed (very slowly) so bear with me.

Cheers, Keith Walker

Hi Keith,

Well done getting your system up and running and going to the trouble of launching the associated web site.
I had a quick look at the web site but couldn't see any details of the 3KW power controller, have you designed your own circuit or are you using a proprietary solution? That question also applies to mains filtering.

Regards
John
 
Hi,

I had the same requirements after getting a 2.8kW rent-a-roof scheme installed.

I have designed a circuit that will automatically use the excess power generated by your solar panels. It monitors the load and the generated solar power and uses the difference to control a 3kW dimmer.

I'm sharing my circuit and hopefully this will produce improvements to the circuit for all to use.

Details can be found at www.talkingsolar.co.uk
The website is still being developed (very slowly) so bear with me.

Cheers, Keith Walker

Had a look at your circuit. using precision rectifiers gives a solution but its performance is far from optimal when combined with a dimmer or proportional controller as these do not give a sine wave current which the solar panel inverter does. If you send me a pm with your email address I will send you a circuit using two chips to do the whole job but its not for publication.
 
Hi Keith,

Even though I haven't got round to building one of these yet, I have to say pmcallis circuits are elegant solutions and also answer one of your web site forum questions about how to cope with a system where there is no henley block and PV uses a spare MCB in the existing CU.

Edit: Didn't mean to just big-up pmcalli, all the other contributors pauldreed, inie meanie, echase etc have done sterling work on this forum, if you havent done so already its worth reading this thread from start to finish.

Regards
John

Note to self, "Must get off my a** and build one"
 
Last edited:
Hi Keith,

Well done getting your system up and running and going to the trouble of launching the associated web site.
I had a quick look at the web site but couldn't see any details of the 3KW power controller, have you designed your own circuit or are you using a proprietary solution? That question also applies to mains filtering.

Regards
John

Hi John,

Given time the power dimmer will be on the site. Time seems to be the one thing I'm very short of.
The next part of the circuit is the comparison. This will then give drive an LED which changes the resistance of a LDR (light dependant resistor). This change of resitance controls the 3kW dimmer.

Cheers, Keith
 
Had a look at your circuit. using precision rectifiers gives a solution but its performance is far from optimal when combined with a dimmer or proportional controller as these do not give a sine wave current which the solar panel inverter does. If you send me a pm with your email address I will send you a circuit using two chips to do the whole job but its not for publication.

Hi John,

PM sent.

Very true I don't get a sine wave when the dimmer is chopping the load. But a couple of capitors gives me a rippled (not sure of the term required) dc output. This is compared and used to drive the dimmer.

Before I started of the mains dimmer I had the control circuit driving three leds. Load, solar power and output. It was so sensitive that if the load conditions was just right and my sub-woofer turned up (and the right sort of music, Queen We Will Rock You) the base beat could be seen on the leds. I was amazed! Anyway a chucky capitor leveled things out.

But the circuit still responds to changes in the washing machines cycle.
Videos to follow when time allows.

Cheers, Keith
 
Last edited by a moderator:
Hi John,

PM sent.

Very true I don't get a sine wave when the dimmer is chopping the load. But a couple of capitors gives me a rippled (not sure of the term required) dc output. This is compared and used to drive the dimmer.

Before I started of the mains dimmer I had the control circuit driving three leds. Load, solar power and output. It was so sensitive that if the load conditions was just right and my sub-woofer turned up (and the right sort of music, Queen We Will Rock You) the base beat could be seen on the leds. I was amazed! Anyway a chucky capitor leveled things out.

But the circuit still responds to changes in the washing machines cycle.
Videos to follow when time allows.

Cheers, Keith

The point of it not being a sine wave but part of one is using rectifiers to generate a voltage proportional to current only works when the two elements you are comparing are of the same current waveform shape. In your case with a dimmer type control load you will export at low and high powers and import at mid powers. this can be corrected but a better result is obtained if you use a detection circuit which measures true power then it is independent of load current shape and power factor.
 
Hey there,

Just thought I'd let you know that I updated my web page based on your useful feedback. You can now change the figures it uses to work out the value of the different arrangements and it will highlight the best performing "simple" element choice:

It’s better but would be nice if you made clear that your headline Summary applies to stepped controllers and not proportional ones.

I have a new installation in London where we have put a web based monitor with 3 current sensors on it: PV generation, grid power and power into the immersion. From this I can see that in last week it’s putting 1-8kWh into the immersion per day. As it’s a very rainy week it’s been limited by the amount of sunshine rather than the thermostat cutting out. During the more sunny days, and even those have been very patchy, it's been 6-8kWh.

So I conclude that your 3kWh is too low and that double or treble that is more representative of a typical household as per a Google search of suitable values. But I don’t yet have the demographics of the household so don’t know their water usage compared with yours. I am assuming they are using gas to provide top up.
 
Last edited:
It’s better but would be nice if you made clear that your headline Summary applies to stepped controllers and not proportional ones.

Done.

So I conclude that your 3kWh is too low and that double or treble that is more representative of a typical household

Yep, I understand that, but at the moment the immersion thermostat is stopping us putting in more than 3kWh. When the weather gets warm and we turn off the central heating I'll investigate how long the immersion element is. Also, as the days get longer we can heat the water between each shower / bath in the morning / evening so we might be able to consume more that way.

Thanks for your thoughts.
 
Hi Keith,

Well done getting your system up and running and going to the trouble of launching the associated web site.
I had a quick look at the web site but couldn't see any details of the 3KW power controller, have you designed your own circuit or are you using a proprietary solution? That question also applies to mains filtering.

Regards
John

Hi John,

I haven't put the 3kW dimmer on the website yet. I've also got a filter on the circuit. The circuit overall design is down to me but with a pick and mix from the internet. I've never disned a circuit before. so it may not be the best in the world but it seems to work for me.

Cheers, Keith
 
The point of it not being a sine wave but part of one is using rectifiers to generate a voltage proportional to current only works when the two elements you are comparing are of the same current waveform shape. In your case with a dimmer type control load you will export at low and high powers and import at mid powers. this can be corrected but a better result is obtained if you use a detection circuit which measures true power then it is independent of load current shape and power factor.

Hi,

I agree that once the dimmer is running my load current will be a chopped waveform. I've added some capitors to smooth this out, so I'm comparing two dc voltages (not true power). I have had the circuit running and ended up taking power from the grid.
I've now changed the circuit so that it doesn't start to switch the dimmer on until 500 watts are being generated above the house load. The dimmer is controlled usings a LED, but the is not very goof at using very low levels of power, less that 25% of the waveform.
So I'm wasting some power but I have left the circuit driving a 2kW heater all day and no power has been use dfrom the grid. I will try reducing the 500 watts differential, but this will be trail and error.
I know my circuit is not the best in the world, but it's been a great winter project and my first design project (or should I say pick-and-mix from the internet project).

Cheers, Keith
 
echase quote:

How do you get £0.081/kWh? Is that because in summer you fall below the usage required to get into the cheaper tariff? Not sure how they decide this tariff, is it based on a quarter by quarter usage or averaged over a year?

E.ON calculates the higher tariff on a daily basis ie in my case 900kWh/year divided by 365 (approx 2.5kWh) charged at the higher rate for each day first plus the remaining power used that same day at the lower rate.
 
Hi All

just spent last 2 days reading all 38 pages on this thread!!!

I have a 3.92kW PV array & an air source heat pump.
I been using the heat pump for HW heating for 3 years, which works fine, but would like to add an immersion heater solution as well, to boost HW heating with surplus PV power both when the heat pump is running & when it isn't - it's not an effective solution to run the heat pump on surplus PV power only because of the time it takes for the heat pump to stabilise after startup.
With my current setup my heat pump can be running & I can be exporting to the grid under good solar conditions but equally I can be running the heat pump & importing some or all of the power to run it depending on solar conditions, time of day etc.
Since my PV installation (Nov 2011) I've exported an average of 24% to the grid.
I run 5 CT's - 3 on a Current Cost EnviR & processing 2 minutes data points through Techtoniq Energy Station 2 software.
I process this data daily to give me daily consumption/export figures using OpenOffice Calc to calculate whether I'm importing or exporting (hence the need for 3 CT's)
The other 2 CT's are used with openenergymonitor's EmonTX, EmonGLCD & NanodeRF methods as mentioned by Paul previously.

I have just ordered a Kemo M028N power control & Kemo M150 DC & Pulse converter to experiment with as PWM control seems to be the way to go but would appreciate any feedback.
My plan is to us the Arduino Uno PWM feature to be able to control the power supplied to a 3kW immersion element but haven't seen a suitable sketch yet!!

ps I seem to recall a previous enquiry within this topic from somebody asking whether anyone was using a heat pump - if you're that person reading this, you just found one :)

I'm not an electrical/electronics engineer (mechanical engineering is my forte) so be patient with me
 
Hi All

just spent last 2 days reading all 38 pages on this thread!!!

I have a 3.92kW PV array & an air source heat pump.
I been using the heat pump for HW heating for 3 years, which works fine, but would like to add an immersion heater solution as well, to boost HW heating with surplus PV power both when the heat pump is running & when it isn't - it's not an effective solution to run the heat pump on surplus PV power only because of the time it takes for the heat pump to stabilise after startup.
With my current setup my heat pump can be running & I can be exporting to the grid under good solar conditions but equally I can be running the heat pump & importing some or all of the power to run it depending on solar conditions, time of day etc.
Since my PV installation (Nov 2011) I've exported an average of 24% to the grid.
I run 5 CT's - 3 on a Current Cost EnviR & processing 2 minutes data points through Techtoniq Energy Station 2 software.
I process this data daily to give me daily consumption/export figures using OpenOffice Calc to calculate whether I'm importing or exporting (hence the need for 3 CT's)
The other 2 CT's are used with openenergymonitor's EmonTX, EmonGLCD & NanodeRF methods as mentioned by Paul previously.

I have just ordered a Kemo M028N power control & Kemo M150 DC & Pulse converter to experiment with as PWM control seems to be the way to go but would appreciate any feedback.
My plan is to us the Arduino Uno PWM feature to be able to control the power supplied to a 3kW immersion element but haven't seen a suitable sketch yet!!

ps I seem to recall a previous enquiry within this topic from somebody asking whether anyone was using a heat pump - if you're that person reading this, you just found one :)

I'm not an electrical/electronics engineer (mechanical engineering is my forte) so be patient with me

Chris,

PWM with Arduino is fairly simple ... for an example sketch check examples and fading in the Arduino software. AnalogWrite is available for certain pins and you'll simply map the result of inputs to the output pin.

Regards
 
Hey there,

Just thought I'd let you know that I updated my web page based on your useful feedback. You can now change the figures it uses to work out the value of the different arrangements and it will highlight the best performing "simple" element choice:

How much water can I heat with spare Solar Power?

Hope that helps.

David,
If you have read all the posts on this thread you will be aware that I am marketing a simple SolarHeat controller which does not measure the differential but is cheap(ish) and can be configured to switch at 1.5kW or 2.5kW output. I recommend this type for summer use only.

I have read your web posting with interest - very detailed and scientific but I have some concerns about your basics.
1. As others have said 3kWh is very low for the heat absorption available - either you are starting with less than half a tank of hot water or a short immersion heater - as a typical 100 litres tank requires 9kWh to heat from 10 DegC;
2. Your boiler efficiency may be 70% but this will be degraded by pipework losses and boiler cycling to a more typical 60% in the summer;
3. The orientation of your panels maybe a significant factor in output available so far as low winter sun will not be able to give much generation;
4. Your base load of 800W seems very high, 300W seems more typical - as with all good energy management you should go round turning off things on standby, etc.

Interesting to see how your calculations develop over the next few months as I reckon that 1.5kW differential is break-even with gas and a 4kW system should give significant savings over the summer with a 3kW heater.

TT.
 
echase quote:


E.ON calculates the higher tariff on a daily basis ie in my case 900kWh/year divided by 365 (approx 2.5kWh) charged at the higher rate for each day first plus the remaining power used that same day at the lower rate.


Unless you have a smart meter I assume they don’t know what your daily usage is. So every time they do “know” (quarterly when readings taken or estimated) they will make your calculation and average it over the quarter. So assuming when averaged your daily usage is always >>2.5kWh it means you in reality pay the lower rate for any extra gas you use for water heating. It will only be the higher tariff if you use very little gas in summer, e.g. don’t have gas cooking, so bringing your base load usage without water and house heating below 2.5kWh.

To remind you all the original question was about whether using one unit of gas for water heating was priced at the higher or lower tariff.
 
Unless you have a smart meter I assume they don’t know what your daily usage is. So every time they do “know” (quarterly when readings taken or estimated) they will make your calculation and average it over the quarter. So assuming when averaged your daily usage is always >>2.5kWh it means you in reality pay the lower rate for any extra gas you use for water heating. It will only be the higher tariff if you use very little gas in summer, e.g. don’t have gas cooking, so bringing your base load usage without water and house heating below 2.5kWh.

To remind you all the original question was about whether using one unit of gas for water heating was priced at the higher or lower tariff.

Sorry, maybe my explanation wasn't clear enough.
E.ON's higher rate tariff is 22.27p/kWh for the first 900kWh used in a year; thereafter the rate is reduced to the lower tariff of 10.13p/kWh used in the year.
This doesn't mean you pay at the higher rate until you have used the first 900kWh in the year up front.
They divide 900 by 365 days so each day you pay the higher rate on the first 900/365 (approx 2.5kWh) & then at the lower rate on the remainder of power used on that day.
So every customer pays the same for each days higher rate usage (assuming they use at least 2.5kWh), which, I assume replaces the old daily standing charge that no supplier seems to use any more.
This higher rate daily charge comes out at about £0.55 for the first 2.5kWh thereafter the charge depends on the extra days units used but charged at the lower rate.

The same method is used for charging for gas but with different higher & lower rates to electricity in my case 6.859p/kWh for the first 2,680 kWh used in a year then 2.98p/kWh for the remainder used in the same period
Hope this is a bit clearer?
 
I have read your web posting with interest - very detailed and scientific

Thank you.

1. As others have said 3kWh is very low for the heat absorption available - either you are starting with less than half a tank of hot water or a short immersion heater - as a typical 100 litres tank requires 9kWh to heat from 10 DegC;

Yes, I think we probably have a short immersion. I'll be checking that out when we get a warm day and the central heating stays off! I'm planning to check with an external heat sensor.

2. Your boiler efficiency may be 70% but this will be degraded by pipework losses and boiler cycling to a more typical 60% in the summer;

Agreed - and some folks believe even less. As it happens my old Camray is rated at 70%, but hopefully a newer condensing boiler at something like 93% efficient should come down to around 70% or better when taking pipes and other losses into account.

3. The orientation of your panels maybe a significant factor in output available so far as low winter sun will not be able to give much generation;

Yes, as I mention in the article, the panels are WSW which isn't terribly good. Also, it tends to be cloudy in the Vale of York. On the bright side, in the last month the panels offset 200kWh we would have pulled from the grid, but we did export 130kWh for our neighbours to use - if only there were some way to use that locally ;)

4. Your base load of 800W seems very high, 300W seems more typical - as with all good energy management you should go round turning off things on standby, etc.

Indeed, it is high. Overnight it's down to about 350W but sadly during the day we're in the house. To be honest we get good value from the power we're using and tend to leave large loads until the sun is shining. With two young children who like muddy puddles, plus two adults doing computer-based work at home I sometimes think we are lucky to come in at 800W!

Interesting to see how your calculations develop over the next few months as I reckon that 1.5kW differential is break-even with gas and a 4kW system should give significant savings over the summer with a 3kW heater.

Yes, you could be right. Although my web page says "oil", you could insert values for a gas based system into those text boxes and see what it says. I'm hoping to update it when I have more data - it could be enough to capture 'til the Summer solstice and then double everything up for a rough idea.

By the way, feel free to ask if there's some way of presenting the data that would help explain things you're interested in. Sadly the calculations included over 1million readings each for the house and solar over three months so even if I make my Javascript very fast, it'll stress your computer doing the detailed calculations.

If you have read all the posts on this thread you will be aware that I am marketing a simple SolarHeat controller which does not measure the differential but is cheap(ish) and can be configured to switch at 1.5kW or 2.5kW output. I recommend this type for summer use only.

Sounds like a good plan. Best of luck with your sales.
 
Hi echase and all,, I have one of these £32.00 gizmos,and yes it does do what it says, and works well"ish,,
as echase say's you are constantly wondering if it's set right, I have it on a1800w water boiler which boils in no time, then I have to alter it to run aNight storage radiator, which I rewired so as to put on one element or allthree 2500w, constantly watching the power generated, to see if I can switch onthe other elements, it's not ideal, if I set it to run one element 850w, thengo out and the sun shines I am wasting all that energy.
If you want to run 1KW all the time then I guess its fine.
Waiting for something more intelligent to come along

 
Hi - new to the forum - haven't (unlike some new joiners) spent the full 2 days reading all 39 pages, but I have browsed thro' quite a few, suitably impressed with what seems to have been happening here over the past 18 months. What started out as a simple question, and thoughts of switching in an extra 1kW heating element, seems to have evolved almost into an online multi-participant product development workshop, with some deep discussions and brilliant ideas emerging.

Like others we've just had solar PV installed and have now realised the desirability of using it to heat our water also - at present we have no gas, so water & space heating are all electric (storage heaters for the latter). From the forum discussions I'm persuaded that I need to look beyond the Parsons Switch plus 1kW element towards a fully responsive device that will track the generation and use all the surplus available using the existing 3kW immersion element.

If I understand correctly a couple of the regular posters - echase, pmcalli, and a couple of others - have fairly advanced product designs. Is there an FAQ listing these, or links to obtain more information ? I'd like to get something installed in the next month or so, so I can benefit from the increasing sunshine

Many thanks,


Walter
 
Hi echase and all,, I have one of these £32.00 gizmos,and yes it does do what it says, and works well"ish,,
as echase say's you are constantly wondering if it's set right,

A lot of people posting here are asking me if they can buy one of my ready built units. The best offer I can make is to say that they should be available from back end of this year, unless you also want a PV system, in which case you can buy a PV system with my unit now.

If you don’t want to build your own unit based on the designs offered here my recommendation would be to consider one of these £32 units (altough I have never had one in my hands) and use a less than 3kW load on it. That may recover much of its cost in the next year if you don’t mind constantly fiddling with it and worrying about the electricity you are “incorrectly” using/diverting. Then sell the £32 one on eBay and get one of mine which will pay for itself in much less time than your PV system will and needs no fiddling. That all assumes you have a >3kW PV system and do the installation yourself, otherwise the paybacks change.
 
Inspired by some of the folk on this thread (and elsewhere) I spent some winter evenings putting together a combination of Arduino, Crydom SSR, current and voltage sensor, LCD display etc. and now have the capability to monitor export v import with fully dynamic proportionate load control to match the immersion load to net export from solar PV and the rest of the house. So far so good, and I thought I'd finished the difficult bit! I have a 210L Tribune unvented direct cylinder and can hook this up to the bottom immersion unit, but that still means I'll need a grid top-up if I use lots of water in the evening. What I want to do to finish off my system is to install a second cylinder upstream of my existing cylinder as a pre-heat (which lots of others have mentioned). That way if the sun shines a lot - or shines a little over two days when I don't use much hot water - the pre-heat tank should get hotter than my existing one, so I shouldn't need any grid top up at all, and all surplus generation can be harvested until the pre-heat tank tops out at say 85 degrees. But Heatrae Sadia say installing a pre-heat tank between the reducing valve and their cold inlet is against Building Regs so can't be done. Most of the unvented pre-heat cylinders out there seem to be marketed for use only with combi boilers. Has anyone installed two unvented tanks in series in a way that works for Building Regs? The acceptable alternative is to install in parallel and rely on mixing/ diverter valves but that adds complexity/ cost/ more things to go wrong and lacks the simplicity of a pre-heat.
 
I would recommend reading all the posts. I've just finished making pmcalli's gadget, it does exactly what I want, excess P.V. Going to a 3kW immersion. I would PM him mate, he's extreamely helpfull. Good luck !!
 
Thanks for the recommendation, Whip. I'd seen similar comments on the Forum re: pmcalli's helpfulness. These have been borne out in some PMs between us today ;-). As a result I'm seriously considering his solution, either build or buy built. How easy did you find building & testing the gadget ? How easy was installing it ?
 
Last edited by a moderator:
Hi Walter. Working the circuit out and puting it all on a matrix board, I found quite difficult, as I'm not an electronics man. I did manage to blow both my voltage regulators up lol as I wired them up wrong. The 230v side is quite straight forward. And the testing is not to bad, once you get your head round how it works. Also pmcalli couldn't have been more helpful. Just waiting for my LCD screen now to go on the front. Defiantly the hardest thing I've built, but the satisfaction that it works and I made it, is so worth it!!
 
Whip - Thanks for sharing your experiences. So I guess you are still finalising the kit - let us know you find installing it. Presumably any of these devices need to be located near the meter, for the CT sensor to monitor the net usage, but also in the immersion feed from the consumer unit. How are planning to wire it in ?
 
Hi Walter. It's all finished and working apart from the LCD screen which I can install when I recieve it from china. At the moment it's running a 50w downlight (instead of the immersion)so I can see when it's working. Im still waiting for my plumber to install my 27inch immersion. Fortunately I already have a immersion circuit installed so don't have to worry about that. My box/ gadget is fixed next to my consumer unit with a CT connected to my main incoming tail, within the consumer unit. Hope this helps mate!
 
Whip - I like the idea of connecting the 50W downlight as visual feedback. Something like that might be useful in parallel with the immersion once finalised. We've got a Wattson to monitor our PV & usage at present - we find its coloured visual indication useful for 'at a glance' monitoring.

So are you installing a new 1kW element instead of using your existing immersion element ? I'd understood pmcalli's design tracks & uses all surplus PV, and can work with the existing 3kW immersion element, simply adjusting the power feed to the element to provide what is available ... maybe I've missed something.

Like you I have a separate immersion circuit installed. Presumably you wire the controller in the feed to the immersion from the relevant MCB in the consumer unit (CU) that previously just connected to the line of the immersion circuit. So, how does the 13A socket on the gadget work ? Are the L, N, E feeds from the CU wired directly into the gadget and the element circuit to the plug that goes into the socket on the box ?
 
Walter, Im getting my plumber to install a new 3kW immersion. I have no immersion in my cylinder at the moment.
What I have done is to disconnect the immersion circuit at the 16A MCB in my consumer unit. I have then fed the box with this MCB. Then instead of putting a socket outlet on my box, I've taken the output back into the consumer unit and connected this to my existing immersion circuit. Once I have my LCD installed this will show me how much power I'm importing from the grid or how much excess pv power im producing. I think pmcalli said that once the pv power is 40W more than what the house is using it then sends power to the immersion..
 
Whip - I like the idea of connecting the 50W downlight as visual feedback. Something like that might be useful in parallel with the immersion once finalised. We've got a Wattson to monitor our PV & usage at present - we find its coloured visual indication useful for 'at a glance' monitoring.

So are you installing a new 1kW element instead of using your existing immersion element ? I'd understood pmcalli's design tracks & uses all surplus PV, and can work with the existing 3kW immersion element, simply adjusting the power feed to the element to provide what is available ... maybe I've missed something.

Like you I have a separate immersion circuit installed. Presumably you wire the controller in the feed to the immersion from the relevant MCB in the consumer unit (CU) that previously just connected to the line of the immersion circuit. So, how does the 13A socket on the gadget work ? Are the L, N, E feeds from the CU wired directly into the gadget and the element circuit to the plug that goes into the socket on the box ?

in a word yes. you can wire it direct if you want to but having the plug and sockets makes an easy installation for the sparky.
 
Ah, understood. Everything in our home is run on electricity, so the idea of a water cylinder without an element didn't occur to me ;-).

Thanks for clarifying the installation. Do you have the EMC filter on the MCB feed into the box, or between the box and the immersion element ? Or have you installed one for each ?

Will you mount the LCD on the controller box, or will you link it through into your home, where it'll be more readily visible ?
 
Walter, Im getting my plumber to install a new 3kW immersion. I have no immersion in my cylinder at the moment.
What I have done is to disconnect the immersion circuit at the 16A MCB in my consumer unit. I have then fed the box with this MCB. Then instead of putting a socket outlet on my box, I've taken the output back into the consumer unit and connected this to my existing immersion circuit. Once I have my LCD installed this will show me how much power I'm importing from the grid or how much excess pv power im producing. I think pmcalli said that once the pv power is 40W more than what the house is using it then sends power to the immersion..

I would recommend as a precaution if your are wiring direct to the immersion that you add a fuse to protect the crydom should your immersion go short circuit. its a bit overkill as the crydom is 50A and the cu mcb should trip but the crydom is expensive and a fuse is cheap.
 
Thanks pmcalli that makes sence to fuse it.
Walter the LCD fits onto the box, so in the garage next to my CU unfortunately. Would be good to have a remote one. Maybe my next project. The EMC filter is on the feed to the box.
Wife's just phoned to say my display has arrived!! I know what I'm doing tonight...
Just had a thought, in my airing cupboard I have a 20A double pole isolator for my immersion. I'll change that for a single socket outlet and plug my immersion via a 13A plug
 
Last edited by a moderator:
I'd like to clarify the legal position on installing a solar PV controllers, in terms of the wiring regs.

My understanding is that the controller would need to be installed either (i) by a certified installer or (ii) by myself, but in the latter case I would need to get it checked and approved. Either way, before CE marked products come to market, would an installation of a hand-crafted gadget be approved ?

There could be some subtleties here. For example, if the immersion element were connected via a 13A plug to a dedicated socket (fed from the immersion circuit, not the ring main) I believe that would be OK. In that scenario, however, I could plug a controller in between (except, of course, the difficulty of connecting the controller's CT sensor over a rather long distance).

Comments welcome...sorry if I'm asking an 'awkward' question !
 
Last edited by a moderator:
I'd like to clarify the legal position on installing a solar PV controllers, in terms of the wiring regs.

My understanding is that the controller would need to be installed either (i) by a certified installer or (ii) by myself, but in the latter case I would need to get it checked and approved. Either way, before CE marked products come to market, would an installation of a hand-crafted gadget be approved ?

There could be some subtleties here. For example, if the immersion element were connected via a 13A plug to a dedicated socket (fed from the immersion circuit, not the ring main) I believe that would be OK. In that scenario, however, I could plug a controller in between (except, of course, the difficulty of connecting the controller's CT sensor over a rather long distance).

Comments welcome...sorry if I'm asking an 'awkward' question !

If you put the 13A socket from the cu immersion circuit next to the CU then there isn't a problem. As to long lead on the CT. I have tried 50 Meters of lead and it works fine. the problem is routing the sensor lead. other people have had interference problems but in my circuit the worst that could happen is the interference is integrated into an offset which affects the import/export.
 
Hi Chris


I have been using an Arduino Uno since December to divert surplus solar to two 3kW immersion heaters using a 3.3kVA isolation transformer toggling between 55V and 110V and have been looking to upgrade to a triac circuit using PWM from the Arduino.

However, because of the zero cross sensing and triggering of the triac at 100HZ there was no processing time left for the current sensing and calculations needed to provide the trigger levels using a single Arduino. I believe you may need two Arduino's. A good place to look for a PWM circuit is by Googling “Using Hardware Interrupts to Control A.C. Power” it has notes and a Arduino sketch it also works I have built it.


I am still going to replace my transformer, but with an adjustable SSR and instead of the PWM I am going to step through eight different voltage levels to give me eight loads 100W 200W, 300W, 400W, 500W, 750W, 1,000W and 1,500W. I have found that this is all I needed to keep my water hot and the low loads give me lots of flexibility in the winter when spare solar is in short supply.


Let me know how you get on. If you get stuck I have a sketch that calculates PV and load power using two efergy CT's and a sketch for PWM control (as above) and I even have two spare Arduino's and the opto-isolation PCB, so I could get it operational, but it seems overly complicated.


My eight step system will be easier to build, as all the components are readily available and I was hoping to come up with a simple system that anybody could make for less than £100. And this system will meet that criteria.


Regards, Trader9
 
Last edited:
Hi Chris


I have been using an Arduino Uno since December to divert surplus solar to two 3kW immersion heaters using a 3.3kVA isolation transformer toggling between 55V and 110V and have been looking to upgrade to a triac circuit using PWM from the Arduino.

However, because of the zero cross sensing and triggering of the triac at 100HZ there was no processing time left for the current sensing and calculations needed to provide the trigger levels using a single Arduino. I believe you may need two Arduino's. A good place to look for a PWM circuit is by Googling “Using Hardware Interrupts to Control A.C. Power” it has notes and a Arduino sketch it also works I have built it.


I am still going to replace my transformer, but with an adjustable SSR and instead of the PWM I am going to step through eight different voltage levels to give me eight loads 100W 200W, 300W, 400W, 500W, 750W, 1,000W and 1,500W. I have found that this is all I needed to keep my water hot and the low loads give me lots of flexibility in the winter when spare solar is in short supply.


Let me know how you get on. If you get stuck I have a sketch that calculates PV and load power using two efergy CT's and a sketch for PWM control (as above) and I even have two spare Arduino's and the opto-isolation PCB, so I could get it operational, but it seems overly complicated.


My eight step system will be easier to build, as all the components are readily available and I was hoping to come up with a simple system that anybody could make for less than £100. And this system will meet that criteria.


Regards, Trader9


Hi Trader9

thanks for the info.

I'm still waiting for the Kemo kit to arrive but will post results as soon as I have them.

I also like pcmalli's solution so I don't know which system I will adopt yet but I would prefer a 'continuous' rather than a 'stepped' solution

regards

chris
 
Hi - new to the forum - haven't (unlike some new joiners) spent the full 2 days reading all 39 pages, but I have browsed thro' quite a few, suitably impressed with what seems to have been happening here over the past 18 months. What started out as a simple question, and thoughts of switching in an extra 1kW heating element, seems to have evolved almost into an online multi-participant product development workshop, with some deep discussions and brilliant ideas emerging.

Like others we've just had solar PV installed and have now realised the desirability of using it to heat our water also - at present we have no gas, so water & space heating are all electric (storage heaters for the latter). From the forum discussions I'm persuaded that I need to look beyond the Parsons Switch plus 1kW element towards a fully responsive device that will track the generation and use all the surplus available using the existing 3kW immersion element.

If I understand correctly a couple of the regular posters - echase, pmcalli, and a couple of others - have fairly advanced product designs. Is there an FAQ listing these, or links to obtain more information ? I'd like to get something installed in the next month or so, so I can benefit from the increasing sunshine

Many thanks,


Walter

Hi

I also have had a new system fitted Feb 2012 and have been looking into how to heat the immersion heater but taking into account the electricity used in the house. I have a 4kWp system and am trying to look into the best solution. The Parsons switch won't do what I need it to do. However, just stumbled across a product called solardivert who appear to have an intelligent system which will also run the immersion at half power as well as full power. Anyone know now this compares to the other solutions out there?

Thanks Thomas
 
Hi

I also have had a new system fitted Feb 2012 and have been looking into how to heat the immersion heater but taking into account the electricity used in the house. I have a 4kWp system and am trying to look into the best solution. The Parsons switch won't do what I need it to do. However, just stumbled across a product called solardivert who appear to have an intelligent system which will also run the immersion at half power as well as full power. Anyone know now this compares to the other solutions out there?

Thanks Thomas

I've not come across this product previously, so quickly Googled it. Based on what I read on the website and what I've learnt from this forum I'd make the following observations:

1. More expensive than a Parsons Switch - one webpage comments "10x cheaper than solar thermal" (cited as £4500)

2. A simple 2-step controller, switching the immersion on to take either 1.5 or 3kW, but nothing else - thus better energy capture than a Parsons Switch but not as good as the proportional controllers that pmcalli, echase and others on this forum have in the works.

3. Looks like it works with an existing 3kW immersion element, rather than needing a new extra 1kW one, as does the Parsons Switch

4. ??? Available now, maybe not ???? Not obvious how to buy it, so perhaps they're just creating product awareness while the product is CE certified/tested etc ? If you drop them your email and get a reply on availability, be sure to post it here so we know. If its availability is the same as the proportional controllers then why go for stepped ?

One of my concerns is that once some good CE approved products are out there, and we are all using them, it won't take the utility companies long to realise that their 50% feed-in assumption has gone to pot, and to start visiting to install smart meters...(although of course at present they're probably getting much more than 50%). If this happens, product pricing will need to reflect an RoI in 2-3yrs max. At £450 I wouldn't go for this one...

Walter
 
Last edited by a moderator:
One of my concerns is that once some good CE approved products are out there, and we are all using them, it won't take the utility companies long to realise that their 50% feed-in assumption has gone to pot, and to start visiting to install smart meters...(although of course at present they're probably getting much more than 50%). If this happens, product pricing will need to reflect an RoI in 2-3yrs max. At £450 I wouldn't go for this one...

At 4000 kwhr / year. so 50% at £0.03 / unit= £60 This is the max that you can be paid a year from 4kw system. Even using as much as I can, I still export power so the loss to the supplier would be somewhere between £30 to £50 per year. I am not sure that they would consider this worthwhile fitting export meters and all the billing that goes with it, as they would have to fit them for every body.

Analogue control rules ok! :)
 
Inie - yup, I agree with your numbers. However the issue may not be what they're paying for export electricity theyre not getting, but rather the cost they otherwise have to invest to get those MW of electricity from somewhere else ? That cost could be much higher than the cost of fitting smart meters....
 

Reply to Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
487
The unit only heats water using the programmed boost and when pressed in the 1 2 or Cont boost function. I have checked the off-peak time which...
Replies
7
Views
464
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
Hi All. Its been ages since I have been on here- Fortunately log in details stored on PC. I have just had a new boiler and 210 ltr unvented tank...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock