A bit of an embarrassing question.

I have a regular customer who I enjoy working for. He has asked me to install an EV rapid charger for his avant loader (electric tractor type thing). I always turn down 3 phase jobs as I don't feel I understand it fully, but I'd like to do this job.

I believe this is the charger (400V/32A version) Rapid battery charger, e6 - https://www.avanttecno.com/uk/options/rapid-battery-charger-e6

I have added a picture of the 3 phase supply.

1. Are there any additional tests to do, compared with single phase? Phase rotation etc.

2. Is it simply a matter of connecting L1, L2, L3 from the Henly blocks (or perhaps the 3 phase merlin gerlin board) into whatever the instructions say is needed? (eg 30mA RCD)

3. I get a little confused by the role of the neutral in polyphase. Does the neutral have a role in 3 phase or is it simply there to support single phase appliances?

3 phase supply.jpg
3 phase supply.jpg
 
Last edited by a moderator:
If there are three spare ways in the Merlin board then yes take the circuit from there but you will have to fit a separate rcd as you won't get a four pole rcbo for that board.
I have a job using these boards currently. Do they take the Schneider multi 9s? I assume they do but would rather be sure before buying ten mcbs.
 
A triple pole RCBO would be no use for an EVSE installation.
Completely agree Risteard, but in this case it is just feeding a commando socket so would be ok. However, I've bought a 4 POLE RCD combined with a commando socket and will use a 3 pole MCB in the CU.
 
Completely agree Risteard, but in this case it is just feeding a commando socket so would be ok. However, I've bought a 4 POLE RCD combined with a commando socket and will use a 3 pole MCB in the CU.
Ideal.

Generally an MCB feeding an RCCB is going to be the most realistic option here.
 

Reply to Installing a 3 phase rapid EV charger? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock