If needed then something like this should do and does not need a separate enclosure:I don't think it will need it's own meter as this will be the owners tractor, I will ask him though as he has asked for meters before on other work around the place.
A 3 phase meter! More questions!
Yes, if that is the spec.I've just thought of a bit more in relation to cable size....
Lets say this is the 400V/32A charger.
1. Does each line conductor have to be able to cope with 32A?
Check the cable tables though as the rating for, say, 6mm, is different if single phase or three-phase as more I^2*R losses per bundle.
No your equivalent is 22000 / (3 * 230) = 32A2. I realise we have been given 32A in this case, but if we just had the wattage of the charger (lets say 22kW), is the calculation the same as single phase. I.e 22000/400 = 55A?
If you imagine a star-connected load, then you can see that each L current with the L-N voltage gives you 1/3 of the total power.
The equivalent delta case (400V L-L) is more complicated as each L current is shared by two of the arms (say L1 has loads going to both L2 and L3), and not in-phase to make any calculation simple. Answer is 22000 / (sqrt(3) * 400) and is the "same" (though 400V L-L is not exactly the same as 230V L-N)
TL;DR: So just work with the star model as it gives the same answer!