Search the forum,

Discuss Installing a 3 phase rapid EV charger? in the UK Electrical Forum area at ElectriciansForums.net

I don't think it will need it's own meter as this will be the owners tractor, I will ask him though as he has asked for meters before on other work around the place.

A 3 phase meter! More questions! 🥺
If needed then something like this should do and does not need a separate enclosure:

I've just thought of a bit more in relation to cable size....

Lets say this is the 400V/32A charger.

1. Does each line conductor have to be able to cope with 32A?
Yes, if that is the spec.

Check the cable tables though as the rating for, say, 6mm, is different if single phase or three-phase as more I^2*R losses per bundle.

2. I realise we have been given 32A in this case, but if we just had the wattage of the charger (lets say 22kW), is the calculation the same as single phase. I.e 22000/400 = 55A?
No your equivalent is 22000 / (3 * 230) = 32A

If you imagine a star-connected load, then you can see that each L current with the L-N voltage gives you 1/3 of the total power.

The equivalent delta case (400V L-L) is more complicated as each L current is shared by two of the arms (say L1 has loads going to both L2 and L3), and not in-phase to make any calculation simple. Answer is 22000 / (sqrt(3) * 400) and is the "same" (though 400V L-L is not exactly the same as 230V L-N)

TL;DR: So just work with the star model as it gives the same answer!
 
Last edited:
Something worth considering with three-phase charge points is that the phase sequence should actually be varied between units. So if there is a charge point connected L1-L2-L3 then an additional unit should be L2-L3-L1 or L3-L1-L2. This is to prevent them all pulling off the same phase where the vehicle is only capable of single phase charging. Obviously maintain the phase rotation though.
 
the actual circuit is standard 3 phase from what i can see, not sure if it needs PEN fault or Type A rcd etc as its not a standard ev charger within the code of practice etc.
I'll try and find some specs for the unit, but something like this may be suitable?
Is this the standard price for a 3 phase Matt e, expensive!
 
I'll try and find some specs for the unit, but something like this may be suitable?
Is this the standard price for a 3 phase Matt e, expensive!
Yeah - CEF are actually one of the cheaper wholesalers for Matt:e O-PEN devices.
 
Some more...

In the picture in the OP, you can see a separate small enclosure housing a 4 pole RCD (300mA). This feeds the 3 phase CU (and the agricultural single phase meters) where I will be taking power from. I'm guessing this will be a type AC RCD which is going to be a problem if I then need a Type A (or B) RCD downstream to this for the charger.

Am I going to have to change this RCD to the relevant type? They look like a ridiculous price!
Or, I could take the supply from the henley blocks to the left of the 300mA RCD which have no RCD protection? This seems better, as the cable from the Henly blocks to sub DB will not need RCD protection and I could locate it close to the henley blocks in the same room.
 
Last edited:
I'll try and find some specs for the unit, but something like this may be suitable?
Is this the standard price for a 3 phase Matt e, expensive!
Given the cost of the matt:e and it being a farm could you not get a rod in using some machinery?
Like wise if its being used solely inside then use the pme.
 
Given the cost of the matt:e and it being a farm could you not get a rod in using some machinery?
Like wise if its being used solely inside then use the pme.
A rod may be the way forward as the tractor could be charged outside.
 
Some more...

In the picture in the OP, you can see a separate small enclosure housing a 4 pole RCD (300mA). This feeds the 3 phase CU (and the agricultural single phase meters) where I will be taking power from. I'm guessing this will be a type AC RCD which is going to be a problem if I then need a Type A (or B) RCD downstream to this for the charger.

Am I going to have to change this RCD to the relevant type? They look like a ridiculous price!
Or, I could take the supply from the henley blocks to the left of the 300mA RCD which have no RCD protection? This seems better, as the cable from the Henly blocks to sub DB will not need RCD protection and I could locate it close to the henley blocks in the same room.
Yes the upstream device will need to be at a minimum Type A (assuming DC Leakage protection in the EVSE), otherwise Type B. Obviously also S-type (time delayed).

For example a number of EVSEs I installed for a well-known courier firm I replaced the upstream S-type RCCB for a Type A 300mA for the distribution circuit. This went to a switch fuse and then onto the DBs. I had triple pole circuit breakers in the DBs feeding four pole RCCBs. (It was a TT installation.)
 

Reply to Installing a 3 phase rapid EV charger? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
336
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
I have a single 7kW EV charger that serves three holiday cottage. The supply to it is E7, with the night rate currently at exactly half the day...
Replies
7
Views
3K
Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
969

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top