• If you have electrical work available, then you are in the correct forum.

    Post details of the position you have on offer in this forum. Domestic / homeowners are also welcome to post electrical work they have available on their property. Or you're welcome to seach for a Local Electrician in our directory.

Currently reading:
Electrician Jobs Installing a secondary consumer unit in the garage??

Discuss Installing a secondary consumer unit in the garage?? in the Electricians Jobs area at ElectriciansForums.net

This electrician job is going for grabs, please don't post contact details in this area of the forum. Use the forum messaging system instead.
Reaction score
-1
Morning all,


I am looking to install a secondary consumer unit in my garage, linking from my existing house consumer unit.


The first question is If it is ok to run 16mm2 Twin and earth SWA through my hallway and lounge concrete floor in order to get to the garage or should I be running it through the walls? I intend to run a 60A supply to the garage. I could run conduit in the concrete floor?


Secondly, would it suffice to add a 60A rated RCD to the existing house consumer unit for the SWA to run to the garage. The garage consumer unit would then just have a mains switch and MCBs for each circuit.


I intend to run a ring main for sockets all round the garage, a radial for three florescent lights and potential a radial high amp outlet for a welder.
 
firstly, the SWA itself does notneed RCD protection unless the house is TT earthing. better to fit RCD in garage, then a fault in the garage will trip in the garage, not the house. Secondly, should be no problem burying SWA in concrete floor, but I'd duct it.
you could fit a 63A MCB (house end, non-RCD), then sub-board in garage with RCD and appropriate MCBs.
 
If your running twin and earth you will need rcd protection if depth of cable is less than 50mm deep in walls and floors. There are a few other criteria too you would need rcd protection for. Also you need to know the correct zones for running the cable.

However you don't need rcd protection of the supply cable if your running it in SWA.

Peter

Edit: Bugger beat me to it tel
 
Thank you for your prompt responses.


Can I ask what sort of ducting would be ideal to run the SWA in and why I need the ducting if its SWA?


Do I need RCD protection if I am less than 50mm but in SWA?


In terms of zoning I am struggling to find info as most diagrams show wall and ceiling wiring zones. I am simply going through the hall and lounge floor to the outside.


My house is a new ish one using TN-C-S earthing


Regards,
 
ducting protects the SWA from any possible reaction with the concrete, and also gives it that extra protection from mechanical damage to the sheath. any 2" or thereabouts plastic duct will do. zoning applies mainly to cables buried in walls. there's a perfect diagram in OSG.
 
Said spark needs to do the sub main and the initial circuits ....
After that it's possible for you too make changes to said circuit.

What do you plan to use in the garage?
 
Said spark needs to do the sub main and the initial circuits ....
After that it's possible for you too make changes to said circuit.

What do you plan to use in the garage?
think basic sockets and lights initially, but he stated he was planning on getting a welder. the load of the welder need to be considered before designing the installation.
 
I am an engineer by profession and have a welder, lathe and mill. I need a sub main, socket outlets and lights. Potentially a higher rated fused outlet for a welder. If i were to add more sockets or lights I would hope its something I can do without need it signed off again? As long as I am not adding another circuit to the sub main?

I assume in the garage I can just run the twin and earth clipped straight to the single leaf wall or through conduit?
 
I am an engineer by profession and have a welder, lathe and mill. I need a sub main, socket outlets and lights. Potentially a higher rated fused outlet for a welder. If i were to add more sockets or lights I would hope its something I can do without need it signed off again? As long as I am not adding another circuit to the sub main?

I assume in the garage I can just run the twin and earth clipped straight to the single leaf wall or through conduit?

All electrical work should be carried out in accordance with BS7671, this includes inspection, testing and certification of the work. Notification for the purpose of part P however wouldn't be required for the extension of the circuits if not in a special location.

Clipped direct cables would not be appropriate to the workshop kind of environment, I think the most suitable option would be steel conduit due to the risk of damage to the cables from weld spatter, metal chips and general moving of materials and heavy tools.
 
The welder will be pulling 45 Amps, just checked and the power is 11kw
I assume this is an arc welder? It will most likely require hard wiring into an appropriate rated isolator. During use of the welder you may notice a voltage drop which will cause lights to annoyingly flicker. Long continued use will cost you dearly in your electricity bills. (just some friendly advice)
From experience, if you intend to use this as a "professional" workshop then be aware that the council/authorities may get involved and you will require planning permission.
 
Hi,

Where did you get that 100 Amp from?
If it was on the dno's main fuse housing then the fuse inside could be less.
As your not ment/allowed to pull the main fuse "but people do i know lol" you would need to call you supplier & confirm this.

Michael
 

Reply to Installing a secondary consumer unit in the garage?? in the Electricians Jobs area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top