Discuss EV charge point 6mm cable??? Help! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm cable through pre-existing plastic conduit which has a cable in already and through a void in concrete walls to a sub-consumer unit at the charge point. My very limited knowledge of electrics makes me worry that the cable is not big enough. Also can you site the sub-unit so far from the main consumer unit? The SPD and RCBO will be in that sub-box he says. Advice needed please 😢
 
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm cable through pre-existing plastic conduit which has a cable in already and through a void in concrete walls to a sub-consumer unit at the charge point. My very limited knowledge of electrics makes me worry that the cable is not big enough. Also can you site the sub-unit so far from the main consumer unit? The SPD and RCBO will be in that sub-box he says. Advice needed please 😢
Not enough information given here to help. What size is the charger? (Kw)? Is the existing conduit contained in insulation inside the wall? What type of cable is it? Why do you think it’s not big enough?
 
The second CU can be any distance away from the main one as long as the circuit feeding it is properly designed for the distance.

What size power supply is specified for the charger?
 
In nearly all cases 6mm is a large enough cable, assuming this is a standard domestic tesla EV charger with 7kw output.

Some things to be aware off.
Unlike most EV chargers sold in the UK the tesla unit does not have open pen detection and therefore needs a consumer unit with open pen detection or the supply for the building needs to be on a TT earth, your electrician should know what I am talking about but may not know the Tesla units need to be treated differently.

Any EV charger in the UK needs to be connected to the internet, normally by wifi, make sure you have decent wifi for the charger and car. Many chargers benefit from being able to modulate output to manage overall load on the incoming supply or using excess from solar generation. To do this they need a data connection back to the incoming supply, I don't think the tesla does this but personally I would suggest putting in a supply cable that's combined power and data to be future proof, and or get a data connection to the garage. I would normally do this using EV ultra cable. More expensive but much more future proof.


Also make sure the electrician registers the charger with your DNO, provides an electrical installation certificate and notifies the local authority about the installation.
 
Not enough information given here to help. What size is the charger? (Kw)? Is the existing conduit contained in insulation inside the wall? What type of cable is it? Why do you think it’s not big enough?
The second CU can be any distance away from the main one as long as the circuit feeding it is properly designed for the distance.

What size power supply is specified for the charger?
Thanks for the reply- 7kW
 
Not enough information given here to help. What size is the charger? (Kw)? Is the existing conduit contained in insulation inside the wall? What type of cable is it? Why do you think it’s not big enough?
A1F8C8A9-361E-4F64-9BA1-8790242358FD.jpeg
 
In nearly all cases 6mm is a large enough cable, assuming this is a standard domestic tesla EV charger with 7kw output.

Some things to be aware off.
Unlike most EV chargers sold in the UK the tesla unit does not have open pen detection and therefore needs a consumer unit with open pen detection or the supply for the building needs to be on a TT earth, your electrician should know what I am talking about but may not know the Tesla units need to be treated differently.

Any EV charger in the UK needs to be connected to the internet, normally by wifi, make sure you have decent wifi for the charger and car. Many chargers benefit from being able to modulate output to manage overall load on the incoming supply or using excess from solar generation. To do this they need a data connection back to the incoming supply, I don't think the tesla does this but personally I would suggest putting in a supply cable that's combined power and data to be future proof, and or get a data connection to the garage. I would normally do this using EV ultra cable. More expensive but much more future proof.


Also make sure the electrician registers the charger with your DNO, provides an electrical installation certificate and notifies the local authority about the installation.
 

Attachments

  • 276D311A-6067-4730-AE25-475E7C9C2F3C.jpeg
    432.1 KB · Views: 13
While you could arguably tweak the supply voltage and the slightly optimistic ambient temperature, the main thing affecting this is the installation method of 'conduit'.
What cable type are you considering?
Does it actually need to be in conduit?
How long is the conduit?

For example 4 sq mm SWA clipped direct would happily carry 49 amps (before any derating).
 
While you could arguably tweak the supply voltage and the slightly optimistic ambient temperature, the main thing affecting this is the installation method of 'conduit'.
What cable type are you considering?
Does it actually need to be in conduit?
How long is the conduit?

For example 4 sq mm SWA clipped direct would happily carry 49 amps (before any derating).
Thanks for the response, much appreciated. The conduit is probably around 22m long with a cable already in it. All 22m are buried into the concrete walls, floors, ceilings of the house. Temperature here occasionally hits mid 30s. As I’m calculating from the On-Site Guide18th edition what isn’t correct then? I love the maths around cable selection and thought they were accurate 🙈
 
Just some thoughts as a user. We have both original and type 2 Tesla units installed. They are both limited to 32Kw and that is set on the charger unit and also by the in car system.

We were early adopters and it was clear that a TT system was essential. I have no expertise on cable sizes, but as was suggested above (but I am doing so more forcibly) you will seriously regret it if you don't put in a good data cable and wi fi point very close to the charger. The charger instructions don't make this clear.

The reason is that Tesla release 3 types of update. and they do it quite often. Standard, advanced (beta) and maps. especially for full spec cars with autosteer etc. (Waste of money - don;t spec that.....) Some of these will take quite a while to download, and you really don't want to interrupt that or have it fail on a slow wi-fi if you can possibly avoid it, as you can end up with a blacked out and unusable car for ages (4 or 5 hours). NEVER risk doing the updates during the day when you might want to use the car.

If you interrupt a maps update and it fails, then this ever so helpfully takes out all satnav, maps, destinations and all supercharger location guidance, as well as spotify and sometimes the radio and voice recognition too.
 
Just some thoughts as a user. We have both original and type 2 Tesla units installed. They are both limited to 32Kw and that is set on the charger unit and also by the in car system.

We were early adopters and it was clear that a TT system was essential. I have no expertise on cable sizes, but as was suggested above (but I am doing so more forcibly) you will seriously regret it if you don't put in a good data cable and wi fi point very close to the charger. The charger instructions don't make this clear.

The reason is that Tesla release 3 types of update. and they do it quite often. Standard, advanced (beta) and maps. especially for full spec cars with autosteer etc. (Waste of money - don;t spec that.....) Some of these will take quite a while to download, and you really don't want to interrupt that or have it fail on a slow wi-fi if you can possibly avoid it, as you can end up with a blacked out and unusable car for ages (4 or 5 hours). NEVER risk doing the updates during the day when you might want to use the car.

If you interrupt a maps update and it fails, then this ever so helpfully takes out all satnav, maps, destinations and all supercharger location guidance, as well as spotify and sometimes the radio and voice recognition too.
Thanks for your input. Wi-Fi already available in the garage and I will be asking for the data cable for future proofing.
 
What type of cable will you be using? 22m isn’t a long run, and with certain types of cable there is no need for conduit.
Fair enough, if 6mm is all that will fit in the conduit and that is the only way then you’ll have to spec everything else around the cable rather than speccing cable around charger.
 
Can imagine getting a 6mm through an existing conduit of 22mm with a cable already in might have some challenges in it’s self. Obviously not been to job.
 

Reply to EV charge point 6mm cable??? Help! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
537
I would like to hide the cable to an EV charger. The consumer unit, meter cabinet and charger would all be on the same wall. About 5 metres from...
Replies
19
Views
2K
Hi All, Im quoting to install an EV charger (Dont worry - fully registered, but only been 2 weeks so i'm still picking bits up). Consumer unit...
Replies
1
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
741
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock