Currently reading:
Installing new circuits but RCD failure !

Discuss Installing new circuits but RCD failure ! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

devonsparky

Hi !

I have installed 2 new circuits to a fuseboard (lighting + ring main) for an extension and upon testing have discovered that both the RCD's on the split load board have failed.

Can you still issue a cert with these failures noted or do you have to get them sorted before a cert is issued?
 
Hi !

I have installed 2 new circuits to a fuseboard (lighting + ring main) for an extension and upon testing have discovered that both the RCD's on the split load board have failed.

Can you still issue a cert with these failures noted or do you have to get them sorted before a cert is issued?

Why wouldn't you just replace the faulty units? and everything is then A-ok.
 
If you have added 2 circuits to someone's home and now the RCD's aren't working, I would expect you to get it sorted. If they weren't working before, then tell the homeowner that they have failed and need replacing. Seems odd tho that both would fail...
 
Do you mean failed as in will not turn on since you have added these circuits if so then check where you have connected the neutrals..
Or do you mean failed as in failed on your testing. have you tried ramp testing them??
 
Interesting, I would disconnect the new circuits and test the RCDs. to assure myself that the new circuits have been wired correctly.
I assume the RCDs were working before the new circuits were added?
 

Reply to Installing new circuits but RCD failure ! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock