Hi gang
im currently testing a power station,
ive been told to use method 2 ie link live to neutral and test to earth on all the lighting circuits, which are all in SWA on tray with no switches in the circuits.

all readings ok so far, but the last couple are reading 0.00ohms.

these circuits have emergency light fittings in them but i thought using method 2 bypassed the load, can anyone offer an explanation please?

thanks
 
the e fittings have only 1 supply. in each area there are 2 lighting circuits, 1 from the 'essentill' db and 1 from the 'non-essential' db. the fittings on the essential db are emergencys. could be a cross between the neutrals between the 2 dbs.
 

Reply to insulation resistance test method 2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock