Discuss insulation resistance test method 2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
56
Hi gang
im currently testing a power station,
ive been told to use method 2 ie link live to neutral and test to earth on all the lighting circuits, which are all in SWA on tray with no switches in the circuits.

all readings ok so far, but the last couple are reading 0.00ohms.

these circuits have emergency light fittings in them but i thought using method 2 bypassed the load, can anyone offer an explanation please?

thanks
 
the e fittings have only 1 supply. in each area there are 2 lighting circuits, 1 from the 'essentill' db and 1 from the 'non-essential' db. the fittings on the essential db are emergencys. could be a cross between the neutrals between the 2 dbs.
 

Reply to insulation resistance test method 2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
618
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch...
Replies
9
Views
2K
Was testing a 3 phase DB for storage heating. While testing I noticed I was getting continuity between 2 of the circuits, which were on separate...
Replies
13
Views
2K
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock