Discuss joining two feeds into one consumer unit. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
14
I have two 40A swa cables from my main house consumer unit. This consumer unit serves the whole house and the two swa cables serve two consumer units in an extension. One is upstairs and has very little demand and one is downstairs with a higher demand.
My question is:
Can I add the upstairs swa into the downstairs consumer unit allowing more demand and an appropriate t+e cable back to feed the upstairs cu.
Basically I want to join the two feeds together either in the downstairs cu or another way.

This will be done by a qualified sparky but I just want to know if it is feasable before I hire him.

Thanks

Greg
 
parallel cables are allowed in the regs, however there are some pre requisites that need to be met.
it is worth asking a spark to quote but it may not be worth the effort and you might not save anything in the end.
 
parallel cables are allowed in the regs, however there are some pre requisites that need to be met.
it is worth asking a spark to quote but it may not be worth the effort and you might not save anything in the end.
Thanks James

Could the two incoming cables go into the same main isolator?
 
As above, it is possible but has significant further implications for cable protection, isolation, and selectivity between protective devices if a board fed from another board.

Probably you would be better to look at having the SWA for the highly loaded board replaced with something bigger.
 
That is one of the many issues you may have.
the terminals at both ends will have to be suitable to accept both cables.
the cable run should be the same length, the same size and ideally the same route.

it is not quite a simple as you might imagine.
 
Thankyou all for your help, it seems that it is not such a good idea.
Can I ask if another solution is viable.
The downstairs newish metal cu has about 16 ways. It has one 100A main isolator and two double rcd's - one 80A & the other 63A.
Can this cu be used as two individual ones if I add another 100A isolator?
So the original feed supplies one half of the board and then splice into the upstairs feed to independly supply the other half. I could then balance the loads accross the board.
 
When you say you have 2 off swa cables that are 40A
what size are the cables?
i.e. 3 core 4 square mm?
 
They are 3 core with an outside diameter of 20mm. I assume they are 10mm sq.
If they are 10mm then they would usually be rated at least 60A (depends on thermal environment, etc), however, there may be other factors limiting the capacity such as the voltage drop if very long, or fault disconnection time depending on how it is powered (MCB or fuse, your supply earth loop impedance, etc).

It would be worth getting a professional electrician in to asses the origin supply characteristics, the cable & route, and sub-main protection, as it might be simply a case of changing the feed to a 60A switched-fuse arrangement for the board needing more power.
 
New posts

Reply to joining two feeds into one consumer unit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
824
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
915
Good morning guys Was looking for advice with regards to installing an outdoor consumer unit. Customer is looking for power to be installed from...
Replies
31
Views
853
Hi everyone, a landlord is converting a house into two flats and wants a separate consumer unit for both flats upstairs and downstairs. He also...
Replies
13
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock