I'm now considering 3 phase installation from the grid.

Could I use the 2 buried existing 3 core -10mm sq swa cables in combination for the 3 phase supply from the new meter/cu/fuses to a 3 phase distribution board about 6 metres away in a new outbuilding?

i.e. one cable to carry 3 live & the other to carry the neutral and earth.
 
The requirements for conductors in parallel, which is what you're proposing here, insist that the cables must be of equal length (so that the resistance of each is the same otherwise you don't get equal current sharing). As I'm guessing this won't be the case, by the time you've bashed about making them just so, I strongly suspect it would have been quicker and cheaper to just upgrade the existing cable.
 
i.e. one cable to carry 3 live & the other to carry the neutral and earth.

No you can’t
Devil's advocate mood.
Why not? Neutral will only carry 3 phase out of balance current, so sized to suit the supply fuse rating of one phase, and the other conductor, paralleled with 2 x SWA wire armour should more than cover the earthing requirements.
 
Worst case is that one phase is fully loaded and others are carrying no current

so you now have 2 steel armoured cables carrying the current in one direction each.
the eddy currents will be horrible, it is for this reason that you can’t get single core swa cable.
edit,
single core aluminium wire armour is available and is ok because there is no inductive coupling.
 
Yes, of course, eddy currents.
My excuse is that I've been working all day up in the air in my cherry picker, with the sun beating down. Brain more than a little frazzled.
 
Worst case is that one phase is fully loaded and others are carrying no current

so you now have 2 steel armoured cables carrying the current in one direction each.
the eddy currents will be horrible, it is for this reason that you can’t get single core swa cable.
edit,
single core aluminium wire armour is available and is ok because there is no inductive coupling.
Could this happen anyway with 4 core?
Only one cable will be carrying current in one direction with the other cable carrying the neutral and earth the opposite direction.
 
Yes, of course, eddy currents.
My excuse is that I've been working all day up in the air in my cherry picker, with the sun beating down. Brain more than a little frazzled.
Find a cold beer, it will cool your faulty brain and make things much clearer!!
 
Could this happen anyway with 4 core?
Only one cable will be carrying current in one direction with the other cable carrying the neutral and earth the opposite direction.
In a 4 core you would have 3 phases and a N conductor.
the current will balance out to be equal.
outer armour provides the earth and there should be no current or just a negligible amount.
 
Last edited:

Reply to joining two feeds into one consumer unit. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock