Am just wondering if someone can help me on this "The disc of an energy meter makes 600 revolutions per unit of energy. When a 1000W load is connected, the disc rotates at 10.2 revs per minute. If th load is on for 12 hours, hw many units are recorded as error?" I calculated the % error of the meter to be +1.796%. The answer proooided to the question above is "0.24kWh more".

Can anyone tell me how did they come out to the 0.24kWh?
 
10.2 X 60 X 12 = 7344

7344/600 = 12.24

Actual reading should be 12 so error is 0.24kWh

Giving a meter error percentage of +1.965% which is within current published acceptable tolerances of +2.5% and -3.5%.
 
10.2 X 60 X 12 = 7344

7344/600 = 12.24

Actual reading should be 12 so error is 0.24kWh

Giving a meter error percentage of +1.965% which is within current published acceptable tolerances of +2.5% and -3.5%.

Many thanks for that IQ Electrical, very much appreciate it....
My % error calculation seem to be different from yours???
 

Reply to kWh meter manual testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock