I must be confused about some wording,
Light circuit R1+R2 is 1.84 Ze measured = 0.28
So if I do Ze +(R1+R2) I get 2.06
Maximum Zs allowed is 6.14
actual measured Zs is 0.88
This measured Zs is much lower than the max value, I know higher is not good but lower Zs leads to any problems ??
Light circuit R1+R2 is 1.84 Ze measured = 0.28
So if I do Ze +(R1+R2) I get 2.06
Maximum Zs allowed is 6.14
actual measured Zs is 0.88
This measured Zs is much lower than the max value, I know higher is not good but lower Zs leads to any problems ??