I must be confused about some wording,

Light circuit R1+R2 is 1.84 Ze measured = 0.28

So if I do Ze +(R1+R2) I get 2.06

Maximum Zs allowed is 6.14

actual measured Zs is 0.88

This measured Zs is much lower than the max value, I know higher is not good but lower Zs leads to any problems ??
 
make sure you batteries are not low and that you have good connection with your test leads. could also be parrallel paths make earth loop lower
 
I must be confused about some wording,

Light circuit R1+R2 is 1.84 Ze measured = 0.28

So if I do Ze +(R1+R2) I get 2.06

Maximum Zs allowed is 6.14

actual measured Zs is 0.88

This measured Zs is much lower than the max value, I know higher is not good but lower Zs leads to any problems ??[/QUOTE]



You cant expect your Zs to be bang on the maximum every time....it's a maximum for a reason. If a lower than maximum Zs would be a problem we would have to measure Ze before installing any cables,work out the reistance required to reach the maximum and install a length of cable of exactly that resistance....dont happen does it?
 
Measured is always better than a calculated reading

I agree in a way but if calculated is within spec then no need to measure as you're working on live equipment when it isn't necessary just to gain another still compliant figure. You've already measured Ze so know there's an earth path and you've proved the CPC is continuous.
You're also wasting time by effectively doing the same test again......

You may consider this a little over the top but that in itself would contravene the EAWR section 14(a):

Work on or near live conductors

14. No person shall be engaged in any work activity on or so near any live conductor (other than one suitably covered with insulating material so as to prevent danger) that danger may arise unless–
(a)it is unreasonable in all the circumstances for it to be dead; and
(b)it is reasonable in all the circumstances for him to be at work on or near it while it is live; and
(c)suitable precautions (including where necessary the provision of suitable protective equipment) are taken to prevent injury.
 
I agree in a way but if calculated is within spec then no need to measure as you're working on live equipment when it isn't necessary just to gain another still compliant figure. You've already measured Ze so know there's an earth path and you've proved the CPC is continuous.
You're also wasting time by effectively doing the same test again......

Defo not a waste of time! Ok so you did your R1+R2 test , which you disconnected at the CU, measuring your Zs is the only way to prove you remade the connections properly and also to establish wether or not there is a possible loose connection in the circuit.
Do it Properly
 
Regulations state calculated is an accepted method, and R1R2 tests should be carried out so if you wish to use a calculation or go on and do a live zs either is acceptable - cant see the problem
 

Reply to Lighting Circuit Zs in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock