Fellas
Had a call out to a tripping MCB, 6A Starbreaker, the kitchen lights trip the breaker intermit idly.
The lighting arrangement is 5 X 35w LV Halogens on a wire rail, voltage is stepped down via one 210VA transformer, I tested the cable from the switch (looped N) to the transformer L-N, reading was >600Meg, I removed the lamps and tested the L-N on the rail >500 meg, The transformer was replaced last week by a DIY friend so that is new, no trapped conductors in the switch.
Swapped the 6A starbreaker for one I had in the van, tripped again, replaced it with a 16A as its wired in 1.5mm and it has cured the problem, it’s only a GF flat and there are two lighting circuits, I can’t imagine that half the flat can draw more than 6A?.
I’m going to order a 10A as I can’t be sure it’s wired in 1.5mm throughout and also a type C 6A.
I also couldn’t find any high loads on that circuit, like a DIY socket?
Any ideas?!!
 
a clamp meter would be a good idea. also, there could be an intermittent fault, maybe breaking down when warm?
 
Very strange indeed. I would check that the circuit doesn't supply anything in any other flats. I was once working in a flat, isolated the lot and the kitchen sockets were all still live! They were being supplied from the flat above!
 
Coincidently at a quite today I noticed they had a frost watch heater connected to the light circuit in their entrance hall, apparently it was put there to keep their shoes warm before they put them on.
 

Reply to Lighting fault which I cant explain! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top