Currently reading:
lighting fault

Discuss lighting fault in the UK Electrical Forum area at ElectriciansForums.net

N

Noob2013

Hi all,

I have a strange lighting fault which I'm trying to get my head round. I popped in to a family members house on the way home from work so didn't have a Meggar. However, i had a multimeter and also carried out an inspection and test on this property a couple of months ago and found no problems.

The fault is on the kitchen/dining lights. There is 4 x GU10 3 spot fittings (fitted with the LED GU10s) There is a 2g switch, each switch supplying 2 lights.There are 2 t&e's at the switch (perminent and switch for each set).

Whenever either switch in the kicthen was switched on the mcb trips.

On arrival, several led lamps had physically burnt out and in a right state! Removed all lamps and still tripping!

Disconnected one light from each set and mcb did not trip! Faulty fittings came to mind but 2 at same time seemed odd!

Replaced the lamps in the 2 fittings still connected and the lights came on. After several minutes they tripped so I thought maybe the cheap led GU10s were the cause.

I used my multimeter for supply at the lights instead. The problem I found was that either switch seemed to give a supply all 4 lights even though the switch wires cannot be connected as they are on separate twin and earth's from switch. I can't get my head around it!

Did a bit of testing with my multimeter and all the cables at each light appear to be in the correct terminals. I also testing it a few months ago and found no dead shorts or issues.

With the mcb off, I switched each switch individually and made sure that it was switching the 2 lights it should and not the other 2.iSo dead testing of the switches seemed like there was no interconnection between them and was switching correctly. But when circuit energised all the switch lives had voltage!

One thing I noticed when mcb off, I had 0.8v DC between the 2 switch lives at switch??

The only thing I didn't try was to physically disconnect the other 2 fittings, possibly faulty too?? back feed on neutral???

I am going back with my Meggar to test everything properly but I have recently done this and everything was fine. Just seems odd that the leds were burnt out and 2 fittings were causing the mcb to trip with no lamps in. Any ideas before I return would be much appreciated as I got to the point were I was thinking WTF!

All I can think is the other 2 fittings are faulty too and giving a back feed through the neutral but again doesn't sound possible with lamps removed and there are no electronic parts (only lamp holders)

Thanks
 
Last edited by a moderator:
...well,it's a very common abbreviation,of a device the OP said he was short of...first letter;means "validated",second is the medium,scale or type of an electric characteristic,third is the description of the device role.

And,even on me hols,i always have one to hand:goofy:
 
I live about 10 miles from Hayle, weather's not great for a holiday at this time of the year though. :p

...Now that is a PROPER Cornish understatement!

Got family down this end,so regular visits are made...some Easters are sunbathing on the beach at St.Ives...others are spent chasing 47Kg LPG bottles around Gwithian Sands....but no problems launching the kids kites this year :lol:
 
...well,it's a very common abbreviation,of a device the OP said he was short of...first letter;means "validated",second is the medium,scale or type of an electric characteristic,third is the description of the device role.

And,even on me hols,i always have one to hand:goofy:

Don't know about anyone else, but I need another clue! Daz
 
UPDATE!

So I went back with my Meggar and found the issue!

Tested between the 2 switch lives at the switch and found a short (not picked up on my multimeter)

Started lifting floorboards to trace the cables and found a screw had just caught both switch lves in each t&e where they went through the joist!

These floorboards were lifted a week or so after I carried out the inspection and test!

The switch lives arcing together must be the cause of the LEDs burning out.

Sorted out the damage cables, tested and everything working bang on!

Appreciate all the advice and input given by everyone :)
 
now that's a good result. i assume the cables were just notched into the joists with no mechanical protection. well done for perseverance, and thanks for letting us know the outcome. and welcome to the world of finding awkward faults. :sunny:
 
now that's a good result. i assume the cables were just notched into the joists with no mechanical protection. well done for perseverance, and thanks for letting us know the outcome. and welcome to the world of finding awkward faults. :sunny:

The cables were drilled through the joist (not low enough down though) but also the nails were pretty long.

It's always nice to have a fault and find it! :)
 

Reply to lighting fault in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top