UK Looped Service

Discuss Looped Service in the UK Electrical Forum area at ElectriciansForums.net

Mrtilly

DIY
Reaction score
22
Hi Guys,
I have a looped service in my house, concerned about the cable going next door. It looks old and brittle (I have not touched) . It was installed about 1955, do you think SP Energy Networks would replace the cable
 

Attachments

  • power cable to next door.jpg
    357.6 KB · Views: 129
The conduit containing those wires must be earthed, and well enough to deal with a really big fault. No idea if it is earthed somewhere out of sight though.

The other issue is they are almost certainly VIR (vulcanised Indian rubber) insulated wires. In most cases the rubber perishes and becomes brittle so dangerous if anything causes movement. They might be OK, miracles do happen, but you have the right attitude of not touching them at all.

The results of a short anywhere exposed to you has the very real risk of 3rd degree burns from the arc-flash and possible eyesight damage, not to mention a house fire risk and electric shock.
 
Hi thanks I have sent them a message and photo of it. However I wanted some advice from you guys in case the try to say it's ok.
If they say it is ok there is little you can do other than make a note of the contact with them for future reference, I had something similar a few years ago, I'm surprised they didn't swap the cable when they changed the service head
 
The conduit containing those wires must be earthed, and well enough to deal with a really big fault. No idea if it is earthed somewhere out of sight though.

The other issue is they are almost certainly VIR (vulcanised Indian rubber) insulated wires. In most cases the rubber perishes and becomes brittle so dangerous if anything causes movement. They might be OK, miracles do happen, but you have the right attitude of not touching them at all.

The results of a short anywhere exposed to you has the very real risk of 3rd degree burns from the arc-flash and possible eyesight damage, not to mention a house fire risk and electric shock.
Hi thanks no earth at my end there was but was cut of when they changed the service head. Just had the faulty meter changed (that's another story!) guy said he would also mention the old cables in his report.
 
OP keep us updated, I would be interested what the DNO say/do.
Will do, I will be pushing it if they don't do any thing about it. (just had a problem with my electric meter my energy supplier was not very helpful. So I explained to them if any thing were to happen they would end up court. Result emergency call out on Friday night meter replaced today)
 
SP Energy Networks sent someone out as an emergency to check it. Said it was ok just now but would have to be replaced. Does not understand why it was not replaced when new service head was done. Spoke about putting new cable through conduit. Told him not happy about doing that so said they would probably put in new service for next door. Thanks for everyone's advice on this.
 
SP Energy Networks sent someone out as an emergency to check it. Said it was ok just now but would have to be replaced. Does not understand why it was not replaced when new service head was done. Spoke about putting new cable through conduit. Told him not happy about doing that so said they would probably put in new service for next door. Thanks for everyone's advice on this.
UPDATE Company carried out survey for SPEN saying the preferred option was to keep the looped service. As it a concrete floor in that part of the house (used to store the coal at one time) they would have to go up and over. They want to run the cable up the wall then up the bedroom wall along the loft space and same for next door. Told the was not having that (bat enough with the shower cable taking that route). Spoke to them on the phone today they saying that's the only way as it concrete floor. I would have thought they could bring a new supply up the wall next door and cover with protection plate, so said that to them so they now going to pass it back to Scottish Power Energy Networks
 
I'm surprised they didn't swap the cable when they changed the service head
That would be too easy, the problem is the DNO is split into several divisions all doing their separate bit, it is highly likely the person who upgraded the service head wouldn't have a clue about the need to replace those, nor would the person fitting the meter etc etc... there was once a time many decades ago when they had skilled people who did the job lot and knew their stuff and this would never have been left like that.
 
Stick to your guns. The problem is with next door's supply, not yours. It's not your problem how they get a new supply to next door, nor should it inconvenience you in any way..
If it was a new build next door, they wouldn't be wanting to "run it up your bedroom wall", so don't let them now.
 
That would be too easy, the problem is the DNO is split into several divisions all doing their separate bit, it is highly likely the person who upgraded the service head wouldn't have a clue about the need to replace those, nor would the person fitting the meter etc etc... there was once a time many decades ago when they had skilled people who did the job lot and knew their stuff and this would never have been left like that.
The guy that replace the meter said he would put the cable in the report he had to put in.
 
Stick to your guns. The problem is with next door's supply, not yours. It's not your problem how they get a new supply to next door, nor should it inconvenience you in any way..
If it was a new build next door, they wouldn't be wanting to "run it up your bedroom wall", so don't let them now.
Thanks, yes I have sent an email to SPEN explaining that this is not on.
 
UPDATE Company carried out survey for SPEN saying the preferred option was to keep the looped service. As it a concrete floor in that part of the house (used to store the coal at one time) they would have to go up and over. They want to run the cable up the wall then up the bedroom wall along the loft space and same for next door. Told the was not having that (bat enough with the shower cable taking that route). Spoke to them on the phone today they saying that's the only way as it concrete floor. I would have thought they could bring a new supply up the wall next door and cover with protection plate, so said that to them so they now going to pass it back to Scottish Power Energy Networks
I would have concerns about the safety of having a live DNO cable run internally within the property the way that has been suggested and I do wonder if a risk assessment of that route would consider it safe
 
Thanks, yes I have sent an email to SPEN explaining that this is not on.

Hi Guys,
I have a looped service in my house, concerned about the cable going next door. It looks old and brittle (I have not touched) . It was installed about 1955, do you think SP Energy Networks would replace the cable
OP keep us updated, I would be interested what the DNO say/do.
UPDATE Yesterday new supply put in to house next door and looped service removed from my house.
 

Reply to Looped Service in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock