Currently reading:
Low insulation reading

Discuss Low insulation reading in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
168
Testing a ring earlier and found 0.8M ohm at 250v between (L&N) - E.
This wouldnt be a neon causing this would it as im testing between L N (joined) to E ? I have not yet tested between the three individually.

This low reading is making me hope somethings still connected, there is a digital boiler controller that I suspect is wired into the supply side of a FCU but maybe its not; would this cause a low reading like this ? or anything else to bring back 0.8M ! I tested between (L&N) - E. Thanks all
 
Old house?
Squeaky floorboards?
Have someone step on the squeaks while you are testing. If your reading fluctuates, you’ve got a nailed cable.

Could be a squashed cable behind a socket? Live nicked against screw?

Time consuming, but got to be done.

And if all else fails, CCTV supplied from lighting circuit ;)
 
And the culprit was, an ancient mini florescent in a showpiece cupboard full of plates, plugged in to a hidden socket behind it. Getting better readings now lowest across L/E at 30M, what a result.

Good man - great feed back ........ each time this sort of thing happens you learn ...... and as you learn you become more efficient ............ and thus your confidence will rise and customers will appreciate you more ....
 

Reply to Low insulation reading in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock