Search the forum,

Discuss Mains Gas earthing in the Commercial Electrical Advice area at ElectriciansForums.net

P

pennywise

Have a friend that's currently working on a church complex, building 1 is fed via a 3ph head with the gas meter being located within this building, building 2 is totally seperate and has its own 100amp single phase head and meter. The problem being building 2's gas supply is from building 1, just wondering if they have to be totally separated or two bonding conductors run back from the gas meter to the two heads or run a seperate submain to building 2 from 1. I believe building 1 is PME and building 2 is TN-S which still needs confirming. Cheers
 
Building 1 Gas pipe bonded to building 1 MET.

Building 2 gas pipe at point of entry to building or wherever practical, bonded to the MET for building 2.

There should be an Emergency control valve on the gas at point of entry to building 2, it doesn't matter which side the bond is as both sides are the customers responsibilty
 
Last edited:
That's what I was thinking, but he was getting contradicting info from a tech line. He's the commercial gas fitter so knows that the valve needs installing. Thanks for the input
 
Building 1 Gas pipe bonded to building 1 MET.

Building 2 gas pipe at point of entry to building or wherever practical, bonded to the MET for building 2.

There should be an Emergency control valve on the gas at point of entry to building 2, it doesn't matter which side the bond is as both sides are the customers responsibilty

Just to add a little to Snowheads post.... If the gas pipe passes through/within Building #1 on route to Building #2 then going underground to supply Building #2, you will need to bond this gas pipe as it enters the building and as it leaves the building....
 
good point, eng54. i assume that's because if the pipe were to be cut in building#1, you'd have 2 pipes independently introducing earth potentials into building#1.
 
Just to add a little to Snowheads post.... If the gas pipe passes through/within Building #1 on route to Building #2 then going underground to supply Building #2, you will need to bond this gas pipe as it enters the building and as it leaves the building....

pipe is surface between both buildings
 
pipe is surface between both buildings


I'd still bond on entry and exit, if the gas pipe is surface ''within'' building #1.


We do the same for all our metalic service pipes that enter and exit buildings. Being a hospital, we have a good many more than most buildings, including bulk medical gases, steam, chilled water, fuel oil, to name but a few!! lol!!
 
I'd still bond on entry and exit, if the gas pipe is surface ''within'' building #1.


We do the same for all our metalic service pipes that enter and exit buildings. Being a hospital, we have a good many more than most buildings, including bulk medical gases, steam, chilled water, fuel oil, to name but a few!! lol!!

Yep see what your saying, I'll suggest this happens.
 

Reply to Mains Gas earthing in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
1K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
586
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock